  1. pexhouse

    Question on capacitor size on Trane AC unit

    Thanks for your reply! Here's the capacitor I purchased: http://www.ebay.com/itm/181765656759 The place that was more expensive is a chain that charges a lot. My friend had told me someplace around here sold it much cheaper but I called him several times yesterday (and stopped at his house)...
  2. pexhouse

    Question on capacitor size on Trane AC unit

    Update: I installed the 5mfd in place of the 12.5 and it worked. However I decided to just make sure there wasn't a larger motor installed when the motor was replaced in the past (just had a bad feeling about it) and I managed to see the label on the fan and sure enough it said 1/4 horsepower...
  3. pexhouse

    Question on capacitor size on Trane AC unit

    hmmm I'm still not sure what is going on. Here's an overall picture with a closeup of the dual-run capacitor wiring that is in there now. There's essentially 4 capacitors in there now when the materials sheet shows 3, right? Is one being combined to make a larger one or...??? That one...
  4. pexhouse

    Question on capacitor size on Trane AC unit

    Thanks for the replies! Before I give info to the replies above I just want to say I was thinking and did some searching and came across this: From here: http://homeenergypros.lbl.gov/profiles/blogs/correctly-sizing-a-capacitor This is interesting because the outside A/C unit is either on...
  5. pexhouse

    Question on capacitor size on Trane AC unit

    Hi all, I have a Trane TTX036C100A1 XL1200 A/C unit. I decided to purchase each of the 3 capacitors to have on hand so when one blows I got it ready to go! ...because one blew August last year and it was a $190 service call. ouch Well, when I opened it up I noticed one was leaking. That...
  6. pexhouse

    Correct type of wire to connect to A/C outside unit.

    Thanks for your reply. :) No there's no problem with humidity--it's just a strictly cooling problem. My neighbor across the street has an A/C unit that really cools it down much faster (600 sq ft larger house, but correspondingly larger A/C system...only thing I know about its size is it's on...
  7. pexhouse

    Correct type of wire to connect to A/C outside unit.

    Replacing several runs of wire, including both 240s for the dryer and outside A/C unit. All is good except I'm not sure about the wiring for the outside unit. What is there now is in poor shape and is smashed in the walls between the 2x4s and the brick wall. I don't think there's a linear...
  8. pexhouse

    PEX install on older home using too small diameter pipe?

    ok here is the final how it stands. The 3/4" (squiggly line in drawing) goes all the way to the wall separating the garage from the crawlspace. What that means is that the 3/4" transitions to 1/2" which then goes to the washing machine and then to the hot water heater and then all of the hots...
  9. pexhouse

    PEX install on older home using too small diameter pipe?

    hmmm...I was almost hoping you said that sounded right. lol Most stuff was replaced in the HWH, all the water lines have been replaced in the house. I checked and when hot water is called for the burner turns on nearly right away so it's on the ball. One thing I am thinking about is I...
  10. pexhouse

    PEX install on older home using too small diameter pipe?

    hmm I looked at it and it's a Power Miser 12 and says 40,000BTU/hr and says 40.94 recovery gallons/hr Do those specs seem to fit what I'm describing? or does it still sound like something's wrong? The guy here seemed to agree with me that it seemed to get too cold too quick but maybe we're...
  11. pexhouse

    PEX install on older home using too small diameter pipe?

    ok I talked to the guy and he said they just plumbed it with 3/4" from the meter to the water heater and I believe he said it was 3/4" into the meter so they just went with that and he hasn't had any complaints with the water or the pressure. I don't think I'm going to get any of them to budge...
  12. pexhouse

    PEX install on older home using too small diameter pipe?

    I happened to have today set as a repair appointment for he hot water heater. The thinking is the cold tube in it is broke so it's going to be replaced. We'll him and I get along really well. I even have his home number. His brother is a plumber and they recently redid his home in pex using...
  13. pexhouse

    PEX install on older home using too small diameter pipe?

    I found the beginning VERY interesting because he shows figuring up the developed length included what was under the lawn (from the water meter to the front of the house). On the phone when I was going over what I had I gave him the parts of my addition (meter to house, house to water heater...
  14. pexhouse

    PEX install on older home using too small diameter pipe?

    ok he just called me back and said that the International Residential Code 2009 is what is used for the residential code, whereas the IPC is more for the commercial. I didn't know he was using the IRC and he didn't know I was using the IPC. I do see in the IRC it says a minimum 3/8" can be...
  15. pexhouse

    PEX install on older home using too small diameter pipe?

    I just called up and talked with the inspector and he said that the city hasn't adopted the Appendix (all what I'm showing him is out of Appendix E) and it has to be out of the 'code' (meaning non-appendix) part of the IPC 2009. Can anyone tell me what is going on because I'm lost?!?!
  16. pexhouse

    PEX install on older home using too small diameter pipe?

    I'm mainly clear (imho) on everything except what the pipe under the front lawn (water meter to the front of the house) should be (in reference to the 1" you stated above). I think this is because I am confused by the terms due to me not being a plumber. To put it simply I thought on these...
  17. pexhouse

    PEX install on older home using too small diameter pipe?

    Thanks :) One thing I am not sure on is my understanding of your saying the line from the meter needing to be 1" and not 3/4". I was reading the third row to mean 3/4" service pipe from the meter to the front of the house and 1" distribution pipe under the house for the main trunk. It...
  18. pexhouse

    PEX install on older home using too small diameter pipe?

    It's all OK when just one thing is running. I say OK but in reality I've never seen everything in this house run with a large, clean pipe so not sure if one thing running would work even better with a larger pipe. Currently from what I see where it starts to have problems is when more than one...
  19. pexhouse

    PEX install on older home using too small diameter pipe?

    Ok the inspector came out and took a look. He looked up in the code and can't find anything in it that shows it should be 3/4" and that includes the fixture units. He thinks it would have been better and a good idea to make the trunk bigger but he can't force them on his opinion if it's not in...
  20. pexhouse

    PEX install on older home using too small diameter pipe?

    It was verbal but in reality he did pretty much what he said he was going to do. He told me in the past that permits are included in the price. Never heard anything about a written contract for over $500 or anything of the sort where I'm at. I asked questions but 'assumed' based on the...
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks