    Thermostat recommend with swing/hysteresis adjustment

    They hydrostat sensor inserts into the same old aquastat well and has thermal paste. I confirmed again with thermocouple and I am seeing 10-12 degrees drop between outlet/return. The system has a taco pump 007-f5 and 1" loop. If I reduced flow rate with the current boiler, would that increase...
  2. A

    Thermostat recommend with swing/hysteresis adjustment

    The inlet temp is 127 and outlet is 136 - this was before I raised the temp from 190f to 200. The hydrostat is temp sensor is in well and the inlet/outlet thermocouples are on the pipes right next to boiler. The hydrostat 3200+ has a eco mode setting that tests load by heating up to a lower set...
  3. A

    Thermostat recommend with swing/hysteresis adjustment

    I am not using outdoor reset via the optional hydrostat temp sensor. House is 2500 sqft - half is the first floor and other half walk out basement. Radiators are original 1940 cast iron single zone. I set the boiler to 200F max from its original 190. I have been working on sealing the air...
  4. A

    Thermostat recommend with swing/hysteresis adjustment

    Hi, I have been learning about my Peerless MI-06 boiler and this forum has been an amazing resource - thank you. From what I have gathered here, is that it is overkill for our small house even though it is all brick with poor windows/insulation. I recently replaced the aquastat with a hydrostat...