Well you might want to tell the Black & Decker Corporation that their book is wrong then...
http://books.google.com/books?id=8oS85GWI8OoC&pg=PA44&lpg=PA44&dq=type+L+copper+flared&source=web&ots=8W4S5I-x6A&sig=66Ghf2WekDmRs0V5PpeF7CYXGvw&hl=en&sa=X&oi=book_result&resnum=2&ct=result#PPA44,M1...
nhmaster, thank you for your concern but I respectfully disagree.
I am going to be installing Type L flexible copper gas lines with no connectors.
There will be two flared ends and the entire line will be pressure tested.
From the chart posted, I can see that Type L copper line at 1/2"...
More info from the manual -
Pressure requirements for both units:
Natural Gas:
Minimum Inlet Pressure - 5.0 inches w.c.
Maximum Inlet Gas Pressure - 14.0 inches w.c.
Manifold Pressure - 3.5 inches w.c.
Both fireplaces are Heat & Glo.
The main floor living room fireplace (33 feet from regulator) is a SL-750TR.
BTU's is 16,900 to 24,300 BTU/Hour Input (NG).
The basement fireplace (40 feet from regulator) is a SL-750TRS.
BTU's is 20,200 to 30,800 BTU/Hour Input (NG).
Thanks again!
Thanks for all the replies guys (and gals?),
I understand your concern and appreciate your thoughts.
The fireplace gas input is 1/2". The gas regulator output is 1/2". The furnace, water heater, gas clothes dryer and gas stove are all 1/2".
My plan is to buy 33 feet and 40 feet of...
Good day,
I am installing two new Heat-n-glo fireplaces. I need to run gas lines to both locations.
Here in Mn, 1/2" flexible copper is allowable under code.
One fireplace is approximately 33 feet from the regulator and the other is approximately 40 feet.
Being that copper is so...