  1. B

    Cut-in / Cut-out points WAAAAY apart

    I took Pumpman's advice and installed a new 30/50 switch. It works perfectly right out of the box. Smooth, constant pressure once again. :) I can't believe I spent all that time screwing around with a bad switch.
  2. B

    Cut-in / Cut-out points WAAAAY apart

    As I said, the little screw doesn't come into play here, since it isn't even touching the tension spring. If I were to tighten it, that would only increase the difference in the in/out points, right? As for the bladder tank pressure, I set it to 28 lbs., or 2 lbs less than the cut-in point I...
  3. B

    Cut-in / Cut-out points WAAAAY apart

    This is a very useful forum indeed. I know very little about plumbing, or even specifics about what is in my basement. I have a well with an in line pressure pump. My problem is with the pressure pump switch. I can't seem to get the cut-in/out points set to a reasonable range. 30-50 would...