Recent content by Alfred

  1. Alfred

    Double vanity and laundry in 2" PVC

    I will scope the line and see how easy it is and make the decision at that time. Thank you for guiding a novice through the intricacies of the code.
  2. Alfred

    Double vanity and laundry in 2" PVC

    Just to make sure I am understanding you correctly if the drain line that penetrates the slab was 3" instead of the current 2" right before it goes into the long sweep it would meet the IPC 2015 rules? I will need to verify what size line runs under the slab that feeds this line. Thanks, Alfred
  3. Alfred

    Double vanity and laundry in 2" PVC

    Thank you Wayne, In my city we are under the IPC 2015 as of right now. I appreciate the input and will try to figure out another solution that will meet the IPC standards. Hopefully nothing too drastic.
  4. Alfred

    Double vanity and laundry in 2" PVC

    I am in the process of remodeling a bathroom and would like to add laundry to the same room. The only drain available to me is a 2" line that is currently being used just for the vanities. I would like to add the laundry, be up to code, and not have to replace anything under the slab. I would...