Good morning,
Does anything prevent me from splicing (with a split bolt) a #6 grounding conductor (outside of an electrical box) that bonds the incoming cold water pipe with the nuetral/ground bus in the main service panel?
Can I bond the conductor going to the ground rod to the conductor mentioned above outside of the electrical panel and using a split bolt?

Thanks,
Jason

split-bolt.jpg
 
Last edited by a moderator:

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
While I don't know the answer...I am curious as to why you want to do this.

Does the ground rod wire go to the panel or is it broken or something else?
 

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
0
Location
Columbus, OH
Because that is how it is currently done and when I put in my new panel, I think the existing conductors will be too short and I do not know if they need to be replaced.

Thanks,
Jason
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
Lets see if I understand...you have 2 wires, a ground rod wire and water pipe ground wire both going from the panel box to their respective termination spots but they are bonded / connected together somewhere inbetween with a split bolt.

Is this correct.
 

Got_Nailed

DIY Senior Member
Messages
276
Reaction score
0
Points
0
If you have already met your earthling (grounding) requirements then I think you could if…
Call it bonding the water lines.
The ground rod wire would have to be one peace.
I would think it would have to be in a box but I don’t know.

You could use a ground rod clam and clamp it to the ground rod instead. But it sounds like you came up short on the wire so that might not work. You have to bond the water pipe within 5 feet of the entrance of the water pipe if it is metal on the outside of the house. You might be able to slide it down a few feet. If the water pipe is not metal out side of the house you should be able to bond it anywhere.

I can’t think of any thing in the NEC that would not let you do that.

Remember I’m a plumber but did deal with some electrical stuff and at one point I did know most of the 2005 but never understood it all.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
Good morning,
Does anything prevent me from splicing (with a split bolt) a #6 grounding conductor (outside of an electrical box) that bonds the incoming cold water pipe with the nuetral/ground bus in the main service panel?
Can I bond the conductor going to the ground rod to the conductor mentioned above outside of the electrical panel and using a split bolt?

Thanks,
Jason

The metal incoming cold water pipe, if at least 10 ft long in contact with the earth, is a Grounding Electrode per 250.52.

Any additional ground rod is a Supplemental electrode per 250.53(D)(2).

The conductor connecting the Grounding Electrode to the grounded conductor at the service panel is a Grounding Electrode Conductor per 250.24(D).

The size of the Grounding Electrode Conductor must meet the requirements of Table 250.66. A #6 copper GEC may be used if the incoming ungrounded (hot) conductor is not greater than 1/0 copper or 3/0 aluminum, which are the minimum sizes for a 175 Amp service. If the service is 200 Amps you need larger supply conductors and larger GEC.

250.64 Grounding Electroed Conductor Installation.
250.64(C) requires that the GEC be continuous, or spliced with irreversible connectors or welded.

250.53(D)(2) permits the supplemental electrodes to be bonded to the GEC, so connecting the bonding jumper from the supplemental electrode to the GEC with a split bolt, outside a box, is permitted.
 

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
0
Location
Columbus, OH
Armed with my copy of the 2005 NEC, let's see if I can follow.

The metal incoming cold water pipe, if at least 10 ft long in contact with the earth, is a Grounding Electrode per 250.52.

Any additional ground rod is a Supplemental electrode per 250.53(D)(2).

Per 250.50 these become my grounding electrode system. 250.53(E) states that the connection to my supplemental system shall be #6 copper. I don't know if 250.53(D)(2) has to apply if I consider the ground rod to be the grounding electrode and the water pipe supplemental.

The conductor connecting the Grounding Electrode to the grounded conductor at the service panel is a Grounding Electrode Conductor per 250.24(D).

I'm not sure how this applies. :confused:

The size of the Grounding Electrode Conductor must meet the requirements of Table 250.66. A #6 copper GEC may be used if the incoming ungrounded (hot) conductor is not greater than 1/0 copper or 3/0 aluminum, which are the minimum sizes for a 175 Amp service. If the service is 200 Amps you need larger supply conductors and larger GEC.

That doesn't seem right for residential service. If you see 250.66(A), it says that it need not be larger than #6 Cu if connected to the ground rod.

250.64 Grounding Electroed Conductor Installation.
250.64(C) requires that the GEC be continuous, or spliced with irreversible connectors or welded.

Yes, I see that. Maybe I can solder the connections (with a torch). Would crimp be irreversible?

250.53(D)(2) permits the supplemental electrodes to be bonded to the GEC, so connecting the bonding jumper from the supplemental electrode to the GEC with a split bolt, outside a box, is permitted.

I see how it says that it needs to be bonded, but I don't know where you get that it's ok out of a box w/ a split bolt.

Thx
Jason
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Good morning,
Does anything prevent me from splicing (with a split bolt) a #6 grounding conductor (outside of an electrical box) that bonds the incoming cold water pipe with the nuetral/ground bus in the main service panel?
Can I bond the conductor going to the ground rod to the conductor mentioned above outside of the electrical panel and using a split bolt? Thanks,
Jason

250.64 mandates how the Grounding Electrode Conductor (GEC) is to be installed. It is also important to understand what a GEC is. Any conductor that originates in the panel or meter base and lands on an electrode is a GEC.
To install a conductor from the meter base to a rod and then from the panel to a metal water pipe as described in 250.52(A)(1) would constitute two GECs.
To install a conductor from the panel to a metal water pipe as described in 250.52(A)(1) and then go from the water pipe to the ground rod only one GEC conductor would be installed and the conductor from the water pipe to the rod would be a bonding jumper.

250.64 mandates that a GEC be continuous and without splice and the use of a gas torch and solder would not work for a exothermic weld.
250.53(C) mandates the installation of the bonding jumper. Here we are referred to 250.64(A),(B) & (E). There is no mention of 250.64(C) therefore the bonding jumper can be spliced.

In the case you have described above the simple answer to the question is NO!
 

KD

New Member
Messages
207
Reaction score
0
Points
0
Do not solder any electrical installations. (Appliances, tools, etc. can be soldered. ) Code legal methods are crimp or exothermic welding. Some parts houses will sell you Crimp fittings and rent you a crimp tool with a huge cash deposit. Another method is exothermic welding. This is mixing chemicals in a crucible and then igniting them. Full face mask, gloves, and non-flammable clothing is required.
Ask your inspector if you can use a barrel type compression connector or split bolt and them shrink wrap it so it cannot be taken apart without cutting (the shrink wrap). If there is no inspector.......

split-bolt.jpg
 
Last edited by a moderator:

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
"Cadwelding" is another term for that type of exothermic welding. (think 'thermite' but without the iron)
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
Good morning,
Does anything prevent me from splicing (with a split bolt) a #6 grounding conductor (outside of an electrical box) that bonds the incoming cold water pipe with the nuetral/ground bus in the main service panel?
Can I bond the conductor going to the ground rod to the conductor mentioned above outside of the electrical panel and using a split bolt?

Thanks,
Jason


You didn't explain this very well.

If the GEC is continuous from the service to the ground rod it sounds like you can split bolt a bonding jumper and take it to your water pipe.

If the water pipe bond wire is the one going to the panel you cannot splitbolt the GEC to it.

It's so much easier when we have all the tools and materials to do the job "right" and not worry about a few feet of wire :)
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
If the GEC is continuous from the service to the ground rod it sounds like you can split bolt a bonding jumper and take it to your water pipe.

If the water pipe bond wire is the one going to the panel you cannot splitbolt the GEC to it.

If there is an underground water pipe with at least 10 ft in contact with earth, that IS the grounding electrode, and the ground rods are SUPPLEMENTAL ELECTRODES. See 250.53(D)(2). "The supplemental electrode shall be permitted to be bonded to the grounding electrode conductor, the grounded service conductor, the non-flexible grounded service raceway, or any grounded service enclosure." There is nothing that requires the supplemental electrodes to be connected in any enclosure. It may be split-bolted to the GEC or the grounded service conductor, or attached to the grounded service raceway or the grounded service enclosure.

split-bolt.jpg
 
Last edited by a moderator:

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,540
Reaction score
358
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Bob NH.....thank you very informative

Bob.....While you are looking up those grounding requirements.......


what does it say when the incomming water line to the home is PLASTIC or pvc some nature??? That certainly breaks the secondary ground for the home....

Or the Water conditioner has been tied into the system with plastic teees and has broken the ground to the city copper water service??

We run into this issue all the time and it seems that the
water heaters in the home somehow get attacked and die a quick death ... the copper ground across the pipes somehow becomming a back up ground for the system...

is their anything that claims would relieve this problem??
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
what does it say when the incomming water line to the home is PLASTIC or pvc some nature??? That certainly breaks the secondary ground for the home....
No, it simply means there is no water pipe electrode to use. You still need a water pipe bond if the water piping system in the house is metallic (copper).
If a metallic water pipe feeding the house did exist it MUST be used as the PRIMARY electrode.




Or the Water conditioner has been tied into the system with plastic teees and has broken the ground to the city copper water service??
The there MUST be a jumper around the plastic fittings or any meter, etc that is removable.
 

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
0
Location
Columbus, OH
Does every metal fitting need to be grounded? What if you ran the house with PEX and then used copper stubouts at the fixtures ... do they need grounded?

Jason
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Another variant: my house was originally plumbed with copper, which failed after 30 years under the slab. The old pipe is still in place, although unused (the house is now plumbed overhead with CPVC), but is still used as the primary electrode.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks