#1
|
|||
|
|||
|
I just installed a PEX manifold system and have significantly lower pressure than I did with my galvanized system. The copper pipe from the street is 3/4, which I transitioned to 3/4 PEX. I ran straight to the water heater and have less than three feet of pipe from the water heater to a five port manifold and also about three feet of water from the T to the water heater to a ten port cold water manifold. There were no leaks that I could find, so i don't think I'm losing pressure there.
What could cause a loss in pressure like this? Thanks |
|
#2
|
||||
|
||||
|
3/4" PEX is smaller then copper sizing.
How many bathrooms do you have? |
|
#3
|
|||
|
|||
|
Two full baths.
In the previous system, the copper transitioned to galzanized as it passed the water heater. How is the diameter of 3/4 galvanized compared to 3/4 PEX? The faucets that are closer to the manifold have much better pressure than the ones furthest away if that helps ID the problem. |
|
#4
|
||||
|
||||
|
|
|
#5
|
||||
|
||||
|
What size is the manifold and the pipes leaving it?
Galvanized could be quite small ID after a long time. It's hard to compare old stuff with new pipe. Could be clean, could be the opening of a soda straw or smaller.
__________________
Jim DeBruycker Important note - I'm not a pro FWIW - Don't try to buy a phone from Nokia on-line |
|
#6
|
|||
|
|||
|
I thought I should have one inch from the meter as well, but it is definitely 3/4. I have enough copper to run it to the water heater and just up to the manifolds. I'll try that and see if it helps.
Thanks |
|
#7
|
||||
|
||||
|
3/4" PEX has only slightly higher capacity than 1/2" copper. What size are the lines from the manifold to the faucets. If they are small, or overly long, that will be the most likely source of your poor pressure.
|
|
#8
|
|||
|
|||
|
From the manifolds to the faucets it is 1/2 PEX. The shorter lines were OK, but the longer ones were terrible.
I replaced the 3/4 PEX with 3/4 Copper and that has helped. The shorter lines now have adequate pressure. I ran 3/4 PEX on my longest run, to the kitchen, but the pressure is sill low. It's about a 30 foot span. I guess I'll have to go 3/4 copper there too..... I've learned a lot with this if nothing else. I plan on building a house in the next few yeas and this is valuable information. Thanks to all those who replied. |
![]() |