Zone not heating, but is showing active

Discussion in 'HVAC Heating & Cooling' started by jbusheyvt, Mar 6, 2012.

  1. jbusheyvt

    jbusheyvt New Member

    Messages:
    6
    I have one Zone which does not seem to want to heat up. My TACO box shows the Zone as active and the thermostat appears to be working as well.

    Some things I tried:
    Swapping thermostat with another verified one
    - doing this had the same issue. troubled zone did not work and working zone did.

    Verified TACO zones by turning each off multiple times and back on
    - troubled zone does light up on the TACO box

    Looked for leaks
    - No leaks found

    Given this I can rule out the thermostat and possibly the taco box. Below are four pictures of my setup:

    1st Picture, the Thermostat Appears to be fine
    [​IMG]

    2nd Picture, The TACO Box
    [​IMG]

    3rd Picture, The troubled Zone (Center)
    [​IMG]

    4th Picture, All Zones
    [​IMG]

    One thing to note, This all seemed to happen at the same time I pulled some electrical wire through the same hole the Thermostat wire goes through, but given the TACO indicator turning on and off with the thermostat I'm chalking that up to a coincidence.
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,319
    Location:
    New England
    Can you feel the circulator pump turning on when the zone calls for heat? Is the pipe hot above the circulator when it is supposed to be on? All it takes is a little bit of air in the zone to prevent the circulator from pushing the water through. Have you tried purging the line for that zone?
  3. jbusheyvt

    jbusheyvt New Member

    Messages:
    6
    How easy is it to purge the line for a novice?
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,319
    Location:
    New England
    No one, easy answer...it depends on what you have and how it is connected. If you're lucky, there are purge valves at the radiators or at the high point in the system. Is the zone that is not heating the one highest up? If so, it is likely air. It's one of those things that you have to be there to see.
Similar Threads: Zone heating
Forum Title Date
HVAC Heating & Cooling Connecting a new radiant heat zone for a garage slab to an existing baseboard boiler heating system Nov 12, 2014
HVAC Heating & Cooling Heating basement baseboard zone + domestic hot water Sep 18, 2011
HVAC Heating & Cooling Reworking Radiant Heating Zones. Does this look right to you? Sep 30, 2010
HVAC Heating & Cooling Converting a manual switch heating zone to a thermostat heating zone Mar 10, 2010
HVAC Heating & Cooling Only 1 of 2 Heating Zones Works Jan 6, 2008

Share This Page