Venting of Standard Vent Boiler

Users who are viewing this thread

ssen105

New Member
Messages
2
Reaction score
0
Points
0
Location
virginia
Hi, I have been told that I have a standard vent boiler installed (I purchased the house a year back) with side of house venting. Is this a problem? Does it need a vertical Line Chimney/can the side way vent be modified? Or do we have to change it to a direct vent boiler?

Thanks

Sam
 

Dana

In the trades
Messages
7,889
Reaction score
512
Points
113
Location
01609
Atmospheric drafted boilers need a vent stack sufficiently tall to achieve the necessary draft pressures, and must extend above the ridge line of the house to limit the risk of back-drafting due to wind. If your side-vented atmospheric boiler has a tall enough stack it can still work. If it simply terminates at the wall somewhere between grade and the eaves, it's a hazard.

Do you have a model name/number for the boiler, and a picture of the venting arrangement from both the inside and outside of the house?
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
35
Points
48
Location
Maine
Hi, I have been told that I have a standard vent boiler installed (I purchased the house a year back) with side of house venting. Is this a problem? Does it need a vertical Line Chimney/can the side way vent be modified? Or do we have to change it to a direct vent boiler?

Thanks

Sam

That depends. If it's an atmospheric vented boiler it needs either a chimney or a power vent.
 

ssen105

New Member
Messages
2
Reaction score
0
Points
0
Location
virginia
>
Atmospheric drafted boilers need a vent stack sufficiently tall to achieve the necessary draft pressures, and must extend above the ridge >line of the house to limit the risk of back-drafting due to wind. If your side-vented atmospheric boiler has a tall enough stack it can still work. If it simply >terminates at the wall somewhere between grade and the eaves, it's a hazard.

>Do you have a model name/number for the boiler, and a picture of the venting arrangement from both the inside and outside of the house?

Thanks. Below is the model detail. The venting system is (sorry I could not attach photos) direct vent which turns to the wall 2 feet above the upper
side of the Heater.

Apollo Hydro Heater, Automatic Storage Water Heater, Model A650YRRTL5, capacity 50G
Input BTU/HR 65000
Max Inlet 14.00
Min Inlet 5.00Max Work Pressure 150 PSI

Hope
 