Suggestions on fixing this

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by Linc, Jul 28, 2006.

  1. Linc

    Linc New Member

    Joined:
    Jul 27, 2006
    Location:
    Illinios
    Attached is a picure of my current ejector pump.

    Notice the 1/2" pvc coming in from the rear, that is a hacked way that someone is piped AC condensate into this pit. It is draining into the pit, with the lid just sitting right on top of the pvc. Obviously, this lid NEVER was closed or flush.

    The left 1.5" pipe is the discharge pipe. The right is the inlet pipe that comes over from the Laundry sink drain. I *believe* the upper part of that pipe is for vent. It extends up into the floor above near the outer wall next to the Kitchen sink drain, but I do not see it under the kitchen sink.

    I will be cutting the rusted out lid off, pulling out the non-functioning ejector pump and replacing the pit and pump with a Zoeller M264 and 18"x30" pit.

    I am looking for your take on how to fix this setup and make it standard. I will be replacing the discharge pipes with 2" DWV pipes.



    Thanks
     

    Attached Files:

  2. Linc

    Linc New Member

    Joined:
    Jul 27, 2006
    Location:
    Illinios
    To be clear on my intentions here.

    I am replacing a standard (non-sewage) ejector pump with a sewage ejector pump and larger basin now (this weekend). I am doing this b/c the pump died and I want to put in a full basement bath soon.

    What I will do later is break up the concrete and install the DWV pipes for the full bath group and tie it into this pit.
     

    Attached Files:

    Last edited: Jul 28, 2006
  3. Sponsor

    Sponsor Paid Advertisement

     

    Attached Files:

  4. Cass

    Cass Plumber

    Joined:
    Nov 12, 2005
    Location:
    Ohio
    What is the trap in back there for? The pipe on the right is the vent and there should not be a trap on the line. Is it the trap for the utility sink on the left? Where are you going to run the condensate line that is under the lid?
    Is this sewage ejector pump hooked up to a toilet?
     
  5. Linc

    Linc New Member

    Joined:
    Jul 27, 2006
    Location:
    Illinios
    Cass, thanks for your quick reply, I appreciate it.

    Yes. That trap is for the utility sink, the trap is not under the sink, but staight pipe over to where you see the trap now.

    Not sure yet - any suggestions?

    Not yet. Right now, I just want to fix the plumbing that is there to make it 'proper' while swapping the broken pump for the sewage ejector pump. For now the sewage ejector pump will only pump non-sewage water.



    -Linc
     
    Last edited: Jul 28, 2006
  6. Cass

    Cass Plumber

    Joined:
    Nov 12, 2005
    Location:
    Ohio
    so is the pump just being used only for the utility sink and condensate line now and does the washing machine discharge into the utility sink?
     
    Last edited: Jul 28, 2006
  7. Linc

    Linc New Member

    Joined:
    Jul 27, 2006
    Location:
    Illinios
    Yes, the pump is only for the utility sink and condensate now. The washing machine does discharge into the utility sink. The water softener also discharges into this sink when it re-generates/charges.

    Thanks again,

    Linc.
     
  8. Linc

    Linc New Member

    Joined:
    Jul 27, 2006
    Location:
    Illinios
    Futher along now...

    I now have the old 18x24 sump pit and broken sump pump out.

    The next 'obstacle' I ran into (all experienced plumbers rolling eyes at this point) was the cast iron pipe that was entering the pit from a floor drain. With this pipe extending into the pit, I cannot get the new 18x30 pit into the existing hole.

    I can think of a couple ways to deal with this. Looking for suggestions.

    Secondly, once I get that figured out, how do I tie the cast pipe into the hub on the 18x30 pit? Remember, this will only function as a sump pit (no sewage) for now.

    Thanks,

    Linc
     

    Attached Files:

    Last edited: Jul 31, 2006
  9. Mikey

    Mikey Aspiring Old Fart, EE, computer & networking geek

    Joined:
    Nov 8, 2005
    Occupation:
    Consumer
    Location:
    Central Florida
    Duh... make the hole bigger :D .
     
  10. Linc

    Linc New Member

    Joined:
    Jul 27, 2006
    Location:
    Illinios
    I know, I know, seemed pretty obvious.:eek:

    But, would you guys suggest making it bigger on the pipe side, or making it bigger on the opposite side near the foundation wall?

    I still will need a way to tie the drain pipe into the 18x30 pit. I did not see any gasket or mechanical fitting on the pit I took out, but it seems if the pipe is just 'directed into' the pit, if the pit backs up, it'll seep into the ground.

    Additionally, once I am ready to tie in the (yet to be built and plumbed) basement bath, that pipe will definitely need a water-tight seal to conatin sewage.

    Thanks again for any assistance,

    Linc.
     
Similar Threads: Suggestions fixing
Forum Title Date
Plumbing Forum, Professional & DIY Advice Suggestions for pipe too short (or too long) Jul 9, 2015
Plumbing Forum, Professional & DIY Advice Hose bib - easy to use, good quality - suggestions needed Jun 25, 2015
Plumbing Forum, Professional & DIY Advice Suggestions for converting to Natural Gas Boiler Jun 24, 2015
Plumbing Forum, Professional & DIY Advice How to replace inline sillcock? Need suggestions. May 12, 2015
Plumbing Forum, Professional & DIY Advice Looking for sink/disposal drain suggestions. Sep 8, 2014

Share This Page