Stove/Range circuit

Discussion in 'Electrical Forum discussion & Blog' started by Randyj, Aug 5, 2010.

  1. Randyj

    Randyj Master Plumber

    Joined:
    Nov 25, 2006
    Location:
    Alabama
    I've got to replace the wiring to a stove, normal type installation, about 25-30 ft from breaker box. What would be the normal size breaker and size wire used for this type 220 volt circuit? It will not be run in conduit. It's just a normal stove with 4 burners and an oven.
     
  2. jbfan74

    jbfan74 Electrical Contractor

    Joined:
    Jun 14, 2007
    Occupation:
    Electrical Contractor
    Location:
    Newnan, GA
    What is the model # of the range.
    It will tell you the min. size circuit.

    I run 6/3 with a ground form my freestanding units, and install a 50 amp breaker.
    You may be able to get by with 8/3 and ground and a 40 amp breaker.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    Any new circuit needs 4-wires, a retrofit can be done with an existing 3-wire circuit (where neutral and ground are connected at the range). All new ones have neutral and ground separate at the range, and all new wiring to it should be that way, too. The size depends on the range, and to a limited degree, the length of the wire. With the length of the run you are considering, length isn't that big a deal so no reason to upgrade it for that. You can use a smaller cb on a larger wire, but can't go the other way. So, you could err on the size of the wire (bigger), and then choose the breaker suggested by the range. Downside is, larger wire costs more. It all depends on the range you choose.

    If you are considering a range hood or a combined hood/microwave, or a hood with heating lamps and a big motor, then run another circuit along with the stove's as well.
     
  5. Randyj

    Randyj Master Plumber

    Joined:
    Nov 25, 2006
    Location:
    Alabama
    thanks... after reading other threads I felt like 8/3 WG aluminum or copper 10/3 WG would do the trick with a 40 amp breaker. It's a standard household range without all those wild bells & whistles...
     
  6. jbfan74

    jbfan74 Electrical Contractor

    Joined:
    Jun 14, 2007
    Occupation:
    Electrical Contractor
    Location:
    Newnan, GA
    Neither one of those cables can support a 40 amp breaker.
    10/3 copper can be used on a 30 amp breaker.
    8/3 AL can only be used on a 30 amp breaker.
     
  7. Randyj

    Randyj Master Plumber

    Joined:
    Nov 25, 2006
    Location:
    Alabama
    Thanks! That's why I came here to ask questions. I'm doing this for someone else. I just got off the phone with him and he already purchased the materials and got 6/3WG and a 50 amp breaker. I guess he asked someone at the blue store but I know he got the same size copper as he had in aluminum.
     
  8. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    It's best to use the size breaker the stove calls for. If the wire ends up being oversized, no problem (as long as it will fit in the breaker!).
     
  9. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    If you are replacing it, then if may be a three wire installation. If so, then you need a new 4 wire pigtail for the range along with a new receptacle.
     
  10. Fubar411

    Fubar411 New Member

    Joined:
    Nov 15, 2007
    Location:
    St Louis, MO
    If he's doing aluminum, make sure he has the nox goop and pays attention to how tight everything is. Also, have to make sure the receptical can be used with aluminum.
     
Similar Threads: Stove/Range circuit
Forum Title Date
Electrical Forum discussion & Blog Disabling a Circuit May 15, 2015
Electrical Forum discussion & Blog 110 volt circuit from 220 outlet Apr 29, 2015
Electrical Forum discussion & Blog Electrical Circuit Larger Than Needed Feb 1, 2015
Electrical Forum discussion & Blog Under-performing circuit panel with two 240V appliances Dec 15, 2014
Electrical Forum discussion & Blog New circuit for gas water heater Dec 7, 2014

Share This Page