securing copper pipe

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by jm66208, Mar 24, 2013.

  1. jm66208

    jm66208 New Member

    Messages:
    97
    Location:
    KC
    Seems like a simple problem, but I'm looking for a secure & professional way to secure these copper pipes. See pic. Copper water lines exiting water heater to the left are new. They must drop down to clear ducting as shown. They will run parallel about 6" away from stone basement wall behind them. Hanging from joists above doesn't seem secure. I'm thinking some kind of L brackets mounted to wall perhaps? I hate drilling into these stone walls though. Sometimes they just start crumbling. The wall has been dry locked so I can hardly tell the mortar from the stones. Suggestions? Thanks!

    Attached Files:

    • pipe.jpg
      pipe.jpg
      File size:
      28.2 KB
      Views:
      337
  2. joemcl

    joemcl In the Trades

    Messages:
    30
    Location:
    Pennsylvania
    4640.jpg H 41VPd2FY18L.jpg You can secure pipes to floor joists. You're best option would be copper clevis hangers, 3/8" allthread, and 3/8 floor and ceiling plate. We use these all the time. They are easily found, even in hardware store.
    Last edited: Mar 24, 2013
  3. jm66208

    jm66208 New Member

    Messages:
    97
    Location:
    KC
    Good suggestion Joe. I am just kinda worried because the pipes will hang kinda out in space, and fairly low. How about doubling up the clevises and hanging in a "v" pattern?
    hanger.jpg
  4. kreemoweet

    kreemoweet New Member

    Messages:
    371
    Location:
    Seattle. WA
    Metal or plastic strapping is perfectly adequate to support those pipes. If you are so concerned about them hanging low, you should have them follow the
    contour of the ceiling and duct, where they can be more ridgidly supported. What's the deal, you got a "special" uncle who lives down in the basement who's
    prone to swinging from the pipes when he gets excited?
  5. jm66208

    jm66208 New Member

    Messages:
    97
    Location:
    KC
    LOL...you never know. I can't follow the ceiling because there is more in the way than my drawing suggests.
  6. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,240
    Location:
    Cave Creek, Arizona
    Screw a couple of pieces of UniStrut channel to the bottom of the duct and clamp the copper tubing to them with isolators inside the clamps. OR use a 3/8" rod "floor plate" screwed to the joist, with a 2 piece "ring hanger" around the copper, and a section of 3/8" threaded rod between them.
    Last edited: Mar 25, 2013
Similar Threads: securing copper
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Securing Copper Tub/Shower Rough-In Oct 13, 2012
Plumbing Forum, Professional & DIY Advice, Tips & Securing a copper pipe riser May 20, 2006
Plumbing Forum, Professional & DIY Advice, Tips & Securing a wobbly PVC stack Mar 18, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Securing Pex and Valves to Joists? Jan 17, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Securing a free standing Victoria & Albert tub Nov 25, 2012

Share This Page