This is not VFD but straight 3 phase from the transformer. Grundfos and Franklin and others sell a box that uses inductive sensing to protect against over and undercurrent, quick cycling, etc. They are quite expensive for what they do. CSV sells one that does a lot of that but not over current (for locked motor or wiring fault).
I've got a motor starter on the circuit with overloads. Would this be sufficient to protect the motor against jamming? Or will it be not sensitive or not quick enough?
Second, if I have a CSV on the pump, the current will drop when the valve is closed. It will be a 25S15-9 pump, FLA is supposed to be 7.3A. The instructions for the Grundfos/Franklin style protector suggest setting the minimum current at a fairly high value, like 75% of running amps. Seems like this will run into trouble with the CSV. How low will the current go when the pump is down to 1 g/m?
Third, the installation as it existed prior to this "clean and press" had an overpressure release on the top of the wellhead. I presume to prevent damaging pressure from reaching the rest of the system in the case of a faulty pressure switch. With the CSV, this can't be there, should it be anywhere? Like after the CSV. Even with the CSV, a faulty pressure switch could in theory run the pressure up too much.
I've got a motor starter on the circuit with overloads. Would this be sufficient to protect the motor against jamming? Or will it be not sensitive or not quick enough?
Second, if I have a CSV on the pump, the current will drop when the valve is closed. It will be a 25S15-9 pump, FLA is supposed to be 7.3A. The instructions for the Grundfos/Franklin style protector suggest setting the minimum current at a fairly high value, like 75% of running amps. Seems like this will run into trouble with the CSV. How low will the current go when the pump is down to 1 g/m?
Third, the installation as it existed prior to this "clean and press" had an overpressure release on the top of the wellhead. I presume to prevent damaging pressure from reaching the rest of the system in the case of a faulty pressure switch. With the CSV, this can't be there, should it be anywhere? Like after the CSV. Even with the CSV, a faulty pressure switch could in theory run the pressure up too much.