Need to verify appropriate size of softener

Discussion in 'Water Softener Forum, problems, installation and r' started by 606zpx, Jul 30, 2010.

  1. 606zpx

    606zpx New Member

    Joined:
    Jul 10, 2010
    Location:
    Savannah GA
    Alright...I sincerely appreciate the assistance:

    2 full bathrooms-regular shower heads
    2 people, 3 dogs
    Wash boat and car at times
    may run d/w and/or washing machine while showering
    3/4 copper coming into house
    City water, 6gpg

    Looking at Aquapure softeners (Clack ws-1 cs head) see PDF

    http://aquapure.com/apspecs/LITAP880CWS.pdf

    From a grain standpoint a 0.75cuft would suffice but probably need 1cuft for flow rate and possible growth in number of people (which would make it more likely that both showers would be running while someone is washing a car, etc).

    ALSO....the aquapure guy suggested a sediment filter but I have not seen this as a standard suggestion....truly necessary with city water.......I have not noticed a significant sedimentary issue.
     
  2. Bob999

    Bob999 In the Trades

    Joined:
    Jul 4, 2009
    Location:
    Pennsylvania
    I would go with the 1 cubic foot.

    Set it up with 3 lbs of salt/regeneration and 12000 grains capacity. 14 day override. Program P7. I would not install a prefilter--it is not necessary.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
Similar Threads: Need verify
Forum Title Date
Water Softener Forum, problems, installation and r Need help designing water treatment system Yesterday at 11:12 AM
Water Softener Forum, problems, installation and r I need an iron/sulfur filter Wednesday at 7:58 AM
Water Softener Forum, problems, installation and r Received water test results. Need advice Aug 17, 2016
Water Softener Forum, problems, installation and r Lab results in, recommendations needed. Aug 15, 2016
Water Softener Forum, problems, installation and r Need Setting Confirmation for new FleckSXT Installed Aug 6, 2016

Share This Page