Navien Tankless Water Heater Comments and questions

Users who are viewing this thread

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
JM, a few thoughts to ponder:

How many Rinnai's do you install per year? Does not the Rinnai have better water temperature control and higher flow rates? Doesn't it cost a couple hundred bucks less and have better tech support?

For efficeincy, if you have a car that gets 30mpg and one that gets 35mpg, and they are both in the driveway "OFF" which one is getting better milage?

Now I get the PVC vent thing, however if the venting is up and out the Rinnai is still less expensive with an easy push joint vent kit and a much better hot water source. These things only run for minutes a day, the rest of the time they are off. I think 90+ is over rated for tankless. Seems to me that tgemperature control and flowrate matter more.

80+ is (quite literally) overrated for most tankless in most installations due to the particulars of the EF test: 10.2 gallon minimum draws are nothing like real-world use, and the short-cycle losses for sub-2 gallon draws erodes efficiency dramatically. In real-world draw profiles 0.82EF type tankless units hit in the mid-70s, condensing versions scoring 0.90+ EF numbers run in the high-70s/low 80s. The higher thermal efficiency isn't worth (much) extra for. (Indeed, you'd get better return in fuel savings on drainwater heat recovery on the main shower for the price-delta on the high/mid efficiency units themselves, vent costs not included.)

Steady-state thermal efficiency is a theoretical upper limit, but not a good measure of the real-world performance. Those with tight controls over flue purge cycles losses will do better than those that don't. Those with small header tanks to mitigate cold water sandwich issues that also inhibit fire when the header is above a minimum temp will also suffer fewer cycles, and thus lower purge-losses from multiple low-volume draws, etc. Steady state thermal efficiency or raw combustion-efficiency numbers are only relevant for very large or continuous-draw duty (pool heating, anyone?), not domestic hot water for typical household use. In space heating, commercial laundry/car-wash, health-club showers, or home solar-backup you might beat 90% with a condensing tankless, but not very often (if ever) in straight-ahead DHW apps.


BTW: A a question for any of you who have taken (or will take) the tech courses from various tankless vendors: Is there a modulation level where they typically peak out on raw combustion/thermal efficiency? Do any vendors share any of that data?

Condensing versions likely peak at lower fire in 25-35% of full-fire range (like most mod-con boilers), but I suspect the single heat exchanger types may do better at the high range (like copper-tube boilers), and may be under 80% for raw combustion efficiency at the low end of the modulation range, but 85%+ in the mid/high range. I could as-easily believe the designs have been tweaked to provide peak efficiency at some other burn level, but haven't been able to find test data (which I'm sure is quite proprietary when tested by the manufacturers). Can anybody either confirm/disabuse me of those guesstimates?
 

SewerRatz

Illinois Licensed Plumber
Messages
1,681
Reaction score
10
Points
38
Location
Chicago, IL
Website
www.a-archer.net
In another thread I posted a comparison between Noritz and Rinnai, its only fair I post the Noritz Condensing unit (PVC venting) against the Navien.

noritz.jpg
 

Dovels INC.

New Member
Messages
7
Reaction score
0
Points
0
Location
Virginia
i have had nothing but problems with navien /// not the water heater but with the warranty /////david mills is a jerkoff and is the man incharge of warranty dont do any warranty work because you wont be reinbursed for your expences let them send there man from the factory so so he can fix it ////im not sure wich brand im going to but im sure i wont sell any more navien
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
sounds litk you are not happy with navien

i have had nothing but problems with navien /// not the water heater but with the warranty /////david mills is a jerkoff and is the man incharge of warranty dont do any warranty work because you wont be reinbursed for your expences let them send there man from the factory so so he can fix it ////im not sure wich brand im going to but im sure i wont sell any more navien


I guess that you sell and install this brand??
sounds like youi have been hung out to dry
by their warranty department...

 

Dovels INC.

New Member
Messages
7
Reaction score
0
Points
0
Location
Virginia
I sold 22 units in the last 2 months I'm selling Rheem now so let say Navien is typical Korean company that has great sales department and won't backup anything they say because they hate America and the American people. I told them to pack there shit and move back to Korea
 

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
Oh come on

A quick and easy D&B business search of Dovels Inc, returns it as one-man shop with maybe a helper

22 units, sure!

Sounds like a new installer to me that screwed it up

Take his input with a huge grain of salt!

I like all the Jap platform units with each one having it's better parts, but keep an eye on Navien, they didnt move to position #2 in North America recently in sales, behind Rinnai for no reason.
 
Last edited:

Dovels INC.

New Member
Messages
7
Reaction score
0
Points
0
Location
Virginia
I'm a 4 man shop and 22 units is not that many in 1 month. i own a business how about you. and I agree with most of the people on this forum about navien that's why I'm selling the reem tankless. which is good because I also sell rheem heating and airconditioning. the only reason I posted here is so other businesses don't get taken by naviens warranty also most businesses go under for unbillable hours but if you own a business you know that
 

Dovels INC.

New Member
Messages
7
Reaction score
0
Points
0
Location
Virginia
lol zl100 sounds like a navien rep to me its funny when you tell a company that everbody is bashing them on the internet how defencive they get and navien dose have a good product just shitty customer service and if you are a business owner you know how important customer service is so take that with a grain of salt also
 

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
SewerRatz,

Google "Rannai problem, Bosch problem, Noritz problem"

You will get as many or more complaints about them.

It appears all tend to be plagued by application and install problems.
 

Dovels INC.

New Member
Messages
7
Reaction score
0
Points
0
Location
Virginia
well im just an installer that knows nothing compared to a big eng. like you but the problem is with your tech suport so why dont you put your mind to that problem and tell me how you will fix that. also how can it be a install problem when all you do is hang it on the wall hook up 2 water lines and a gas line plug it in and install a 3 in pvc flue. looks to me that it is over engineered
 

SewerRatz

Illinois Licensed Plumber
Messages
1,681
Reaction score
10
Points
38
Location
Chicago, IL
Website
www.a-archer.net
SewerRatz,

Google "Rannai problem, Bosch problem, Noritz problem"

You will get as many or more complaints about them.

It appears all tend to be plagued by application and install problems.

I did that. I did not find very many complaints about Noritz at all, Bosch I found tons along with Rheem, and Rinnai has has as many as Navain. Navain is still junk. They brag about having a unit with a built in buffer tank. I fell for this till I found out they did it to help with the massive temperature fluctuations these units have and still have with their little built in buffer tanks.
 

flamefix

New Member
Messages
71
Reaction score
0
Points
0
Location
Exeter, England
Can someone confirm to me what you mean by Tankless heaters?

I am assuming you mean instantaneous water heaters.

I fit these all the time, and it is mandatory to fit Condensing water heaters in this country. Often the instantaneous water heaters are central heating boiler combined. We call these boilers combi's for short. Typically they are very efficient.

However, they can only heat so much water by a fixed maximum amount of temperature rise so flow rates will be determined by the cold water main supply and the temperature of the cold water supply. At max demand they pull a lot of gas therefore gas supply pipes need to be adequately sized.

A majority of modern homes in the UK are fitted with a form of instantaneous heating systems. Working with solar as I do and ditting the systems I have I would say if there is only a couple in a small household then Combi is suitable. But large hot water demand storage is better and less gas would be used in a well designed system in my opinion.

A 30kW combi boiler will provide 14 litres/min at 30°C, 12.5 litres/min at 35°C, and 7 litres/min at 55°C rise.

Therefore to get 14 litres at 50c you would need the incoming water to be at 20c.

There is no problem with using these boilers they are generally reliable and having only briefly read through this post the talk about fumes etc seems a bit exaggerated.

Perhaps you might like to read through this article?

http://plumbing-help.net/Introduction to Combination Boilers.html
 

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
Sorry to hear about your Navien woes, my experience has been that they are usually attributed to insufficient gas and changing water pressures. Its no secret that the 98% is achieved by not using a bypass valve in the unit and thus not flashing the water. Which certainly helps in harder water applications.

Having used the Navien, the buffer tank was needed for the mass required to maintain temp for no delay. You see if it was for temp swings it would have been on the outlet, not the inlet water as it is.

Regarding the rest, while I don't care for all the Paloma's, Rheem and Ruud included, I do like the Takagi, Rinnai, and Noritz. In fact my first tankless over 20 years ago was the CEC (later Bosch) Aquastar 170. While not the most efficient it was endless hot water and before Takagi introduced the water bypass valve to the rest, a thermostatic mixing valve made the old Aquastar work quite well. After about 14 years I replaced it with a Rinnai, even though it still worked.

There is no denying that Noritz makes a quality unit, but perhaps being #4 or 5 in the shippment ranks in the US puts their problems with less exposure. Having visited many tankless install jobsites of all brands, perhaps 5% were actual unit problems and the rest install, application, misunderstanding or abuse.

I believe that the day plumbers carry and use a quality manometer to check change and adjust the tankless units the majority of issues for all will go away.
 
Last edited:

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
well im just an installer that knows nothing compared to a big eng. like you but the problem is with your tech suport so why dont you put your mind to that problem and tell me how you will fix that. also how can it be a install problem when all you do is hang it on the wall hook up 2 water lines and a gas line plug it in and install a 3 in pvc flue. looks to me that it is over engineered

What are you rambling about Dovels?

Your procedure for installing a tankless is scary I must say.

Do/can you read the manual?
 

heetmiser

New Member
Messages
2
Reaction score
0
Points
0
Location
NY
And now for my quick rant.
It gets old hearing a navien guy tell us how great his product is, I get it at the wholesaler, from the rep, and from the factory. bottom line is, something in the unit isnt right. first it was the flow sensors, then the board (by the way what generation software are we on now, and how many upgrades is that) now we have plastic elbows failing in the unit (factory recomends stocking a few of these on the truck now,) and meanwhile our customers are getting pretty pissed off.
I did NOT have any (take that back 1) problems with the last brand we installed,(over 100 units) so I dont think its me.
 

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
Welcome to your first post heetmiser (the original is in Colorado)

"I did NOT have any (take that back 1) problems with the last brand we installed,(over 100 units) so I dont think its me."

Curious, why did you stop installing your last brand and what are you using now and why?
 

SewerRatz

Illinois Licensed Plumber
Messages
1,681
Reaction score
10
Points
38
Location
Chicago, IL
Website
www.a-archer.net
Welcome to your first post heetmiser (the original is in Colorado)

"I did NOT have any (take that back 1) problems with the last brand we installed,(over 100 units) so I dont think its me."

Curious, why did you stop installing your last brand and what are you using now and why?

Most guys end up changing brands due to their supply house changing brands. My supply house went from Takagi and Noritz to Navain since Navain has a better price margin for them, I started buying my tankless units at a different supply house now. Granted I have to travel an extra 20 miles to pick up a unit that I know and trust that works, but it is well worth it knowing the peace of mind my customer and myself will have.
 