While the Slantfin tool usually shoots high by about 25%, it's still good enough for sizing ductless heads. It looks like you ran the numbers at 0C/32F whereas the 99% outside design temp for Victoria is actually -3C/26F, which probably cancels most of the internal error for that tool.
The only individual rooms that would call for it's own ductless head are:
Living------------------7832---------------------1/2 ton head
Kitchen & Family-----9940---------------------3/4 ton head
Master----------------6162---------------------- 1/2 ton head
The above could either be done with individual mini-splits, or a 2-ton multi-split, such as the
Fujitsu AOU24RLXFZ with a couple of 7RLS heads and 9RLS head. The combined output of those heads on that compressor would be over 25,000BTU/hr @ -3C, and is still delivering 24,000 BTU/hr @ -8C.
If the living room is adjacent to the kitchen & family that could be combined into a single 1.25 ton head.
The Mitsubishi multi-zone alternative would be the
MXZ-3C24NAHZ , and some FH06 or GL06 heads for the half ton rooms, or a FH09/GL09. (0r with combined zones, a FH15)
The down side to any multi-split solution is that the heads don't really modulate. If you oversize a head by very much for a tiny-load space it can overheat/overcool the room even when "off". When other zones are active there would still be refrigerant pumped through the "off" heads, even though the zone isn't running, with no active blower.
If it's an individual single zone mini-split there could be a rationale for:
Chris Bedroom------3008----------------------half ton
Mitsubishi FH06NA
The FH06NA on a dedicated compressor can modulate as low as 1600 BTU/hr @ +47F, and wouldn't short-cycle on that zone.
With the doors to the smaller load rooms open, with 2-2.5 tons of ductless, keeping the rooms with the heads at a slightly elevated temperature can distribute heat to the other rooms via convection. I have a relative on Whidbey Island (Puget Sound) who heats his whole house with a 1.5 ton single head Mitsubishi, but some of the remote rooms can get a bit chilly when it's -5C out or cooler, even with the doors open.
To make any headway on analyzing the micro-zoned radiant, calculate the room by room floor emittance with 125F water (assuming you're running it all at a single temperature.) If individual rooms can't emit more than half the minimum modulated output of the boiler it's in danger of short cycling unless zones are combined.