Leak in baseboard?

Users who are viewing this thread

MarkLamberti

New Member
Messages
6
Reaction score
0
Points
1
Location
Staten Island
I have a boiler with 4 zones (one of is indirect fired hot water heater)


I finished my basement a few years ago. I put in baseboard using pex for supply in a few spots i ran the pex behind the wall and could not get at it with the pex tool so i used sharkbite fittings.

This winter when the basement zone was running i ran into issues with the hot water loop becoming air bound. I assumed that there is a leak in the baseboard loop i put in.

I finally got around to attempting a fix. I isolated the zone, opened up the fast fill valve and put the pressure up to 100psi. It droped shortly to 90 psi. The problem is i looked at all of the sharkbites and other fittings. I cant see any leaks.

Advise? How is this possible? Is there a leak behind the wall?

thanks
mark
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
If it stabilized at 90psi and didn't drop from there it could just be the PEX flexing or changing volume due to temperature drift. If it just keeps dropping you have a leak.
 