    I am installing a generator transfer switch in the garage.

    My house is long and a main service panel feeds one half and a sub-panel feeds the other half. I want to put the master bedroom on the transfer switch. So, I will have to run it from the subpanel on the opposite side of the house.

    The master bedroom is wired with #14 with a 15 amp breaker. I was thinking of doing the long run (about 80') from the sub-panel with #12 to minimize voltage drop. I would keep the existing #14 in the bedroom with only the #12 providing the feed. It would still have a 15amp breaker. Is intermixing wire size legal? I can put a label in the subpanel on the #12 that says "15amp only/#14 wire in circuit" to avoid confusion in the future.
     
  2. Chris75

    Chris75 Electrician

    Joined:
    Aug 12, 2007
    Occupation:
    Electrician
    Location:
    Litchfield, CT
    Yes, you can use #12 with #14 as long as the breaker is 15amps, and nothing else needs to be done...
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Mr_Magoo

    Mr_Magoo New Member

    Joined:
    Mar 8, 2008
    Thanks for your help
     
  5. Chris75

    Chris75 Electrician

    Joined:
    Aug 12, 2007
    Occupation:
    Electrician
    Location:
    Litchfield, CT
    No problem...
     
Similar Threads: Intermixing wire
Forum Title Date
Electrical Forum discussion & Blog No grounding wire... Jun 22, 2015
Electrical Forum discussion & Blog What size wire for a 230 volt 20 amp breaker? Jun 14, 2015
Electrical Forum discussion & Blog Ground Wire May 20, 2015
Electrical Forum discussion & Blog Wire Color in Conduit May 4, 2015
Electrical Forum discussion & Blog How many wires can I safely fit in 3/4 emt? Feb 28, 2015

Share This Page