How far from a window can a vent stack be? UPC Code

Discussion in 'UPC Plumbing Code Questions' started by Antonio4791, Jul 26, 2010.

  1. Antonio4791

    Antonio4791 New Member

    Messages:
    11
    Location:
    South Pasadena CA
    Hi all,

    I am new here. Hope someone here can answer my question. I am constructing a bathroom within the existing footprint of my home. I am wondering how far from a window a vent stack can be. There is a window nearly directly below where I want to vent. The vent will of course be above the roof, but I need to know how far from the edge of the house it can be. The reason I am concerned is that I have a clay tile roof, which is nearly impossible to walk on. I would like to be install the flashing for the vent by standing on a ladder leaned against the house. But if I get too far away from the roof's edge I cannot do this. Do any codes in California prohibit me from having a vent poke through the roof, say 2-3 feet from the edge of my roof? My city uses California code and doesn't have extra rules.
  2. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Messages:
    810
    Location:
    Penticton, BC
    Someone from your area will probably chime in soon but in most cases you need to be 3' away.
  3. Antonio4791

    Antonio4791 New Member

    Messages:
    11
    Location:
    South Pasadena CA
    Thanks Doherty, 3 feet shouldn't be a problem. Hopefully there is someone from California out there who can verify.
  4. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,686
    Location:
    Cave Creek, Arizona
    There should be no reason why you cannot exit directly above/through the wall, which would place it the distance of the eave from the edge.
  5. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    906.1 Vent shal terminate not less than 6" above the roof nor less than 1 foot from any vertical surface.

    I interpret "vertical surface" meaning such surface rising above the roof, not the edge of the roof. Never had the occasion, so I don't know if that interpretation is correct.

    906.2 Vent shall terminate.....at least 3 feet above any operable door or window.
Similar Threads: window vent
Forum Title Date
UPC Plumbing Code Questions Best transtion(s) from 3" waste stack to 1 1/2" vent stack Sep 3, 2012
UPC Plumbing Code Questions Single Wall Boiler Vent - Combustibles Clearance Oct 27, 2011
UPC Plumbing Code Questions Laundry Room Remodel Using Existing Vent Aug 5, 2011
UPC Plumbing Code Questions Inspector wants full backflow preventer discharge handled by sanitary? Sep 21, 2010
UPC Plumbing Code Questions WC venting, UPC code Aug 3, 2010

Share This Page