    I just had my boiler and pump replaced. 1st and 2nd floor seem to be fine giving heat but the basement rads are cold and they used to be really hot.

    this is my system

    http://highperformancehvac.com/boiler-hot-water-loops.html#monoflow_loop

    my heating guy - doesn't seem to be familiar with monoflow systems. I am suspecting that either the pump is in the wrong direction or maybe the velocity is too slow or too fast to get monoflow t valves to operate.

    The supply loop running along the ceiling is hot as hell but the pipes running to the rads below the supply loop are cold as hell.

    Can you help.
  2. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Purge the air from the radiators.
  3. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,615
    Location:
    Cave Creek, Arizona
    mono-flo

    Posting the MonoFlo site tells us nothing about YOUR system, it just tells HOW it should be installed. Basement radiators could be self venting, depending on how they are connected. For them to operate properly they must use TWO monoflow tees, feed and return, and the flow through them must be in the proper direction, meaning that the return may appear to be backwards if it is not labeled correctly.and they must be adequately spaced to produce a degree of flow resistance between them.
Similar Threads: Help mono
Forum Title Date
Boiler Forum Help Replacing an Old Boiler Sunday at 11:24 AM
Boiler Forum Could use some help figuring something out. Boiler Jun 14, 2014
Boiler Forum Please help me to understand why here is no heat to radiators Feb 23, 2014
Boiler Forum Need help sizing replacement boiler in Connecticut Feb 21, 2014
Boiler Forum Help choosing a control system and manifolds for Hydronic Heating Jan 8, 2014

Share This Page