Gould BF03S pump

Discussion in 'Pumps and Tanks Well Forum & Blog' started by Rick L, May 5, 2012.

  1. Rick L

    Rick L New Member

    Messages:
    1
    Location:
    New Hampshire
    Purchased a camp four years ago. It has a BF03S pump have no idea how old system is. This year had trouble building pressure. Have a high iron content in the water and silt. Decided to start by replacing the point. Hit water at 8 ft and have a total of 18 ft of pipe. That gives me 10 ft of water if my math is not off.
    Still no water, this weekend installed a new pump same model.
    Now here is the problem
    Getting water and pumps shuts off at 40 psi and starts at 20 psi but very slow to recover once you close the faucet.
    On the top of the point I reduced from 1 1/4 to 1 inch and using a 90deg plastic into 1 in black plastic pipe.
    I noticed at the elbow while pump is running that I am getting bubbles. Is that normal.
    Have no leaks around the pump suction or discharge.
    Just no sure about top of point and those bubbles.
  2. LLigetfa

    LLigetfa DIYer, not in the trades

    Messages:
    3,965
    Location:
    NW Ontario, Canada
    Bubbles are not good. Is the sand point included in that 18 feet? If so, the cone of depression might be biting you. If not, you have a leak in the downpipe.
Similar Threads: Gould BF03S
Forum Title Date
Pumps and Tanks Well Forum & Blog Gould BF03S pump with bladder tank Dec 30, 2012
Pumps and Tanks Well Forum & Blog Help with Gould Balanced Flow Pump (BF03S) Feb 14, 2010
Pumps and Tanks Well Forum & Blog CentriPro/Goulds 1AS15 Continous Flow Controller error need help please Feb 11, 2014
Pumps and Tanks Well Forum & Blog Gould J10S w/ Cracked Cast Iron Parts and Other Problems Oct 30, 2013
Pumps and Tanks Well Forum & Blog Ok so I have this ancient Goulds shallow well pump... Sep 27, 2013

Share This Page