Electrical Motor

Discussion in 'Electrical Forum discussion & Blog' started by Fishin, Jun 18, 2010.

  1. Fishin

    Fishin New Member

    Dec 21, 2009
    I have a 115V electric motor that runs a hydraulic cart. After 5 sec of running, it kicks the 20 amp breaker on the wall. It has two capacitors on the side, one start and one run? Would checking the capacitors be the first place to start? We direct wired the motor to an outlet but the results were the same. Thanks.
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Sep 2, 2004
    Retired Systems engineer for defense industry.
    New England
    Look at the data plate for the motor and tell us what the model, voltage, and power numbers say. Did this ever work, or is it a recent problem?
  3. Sponsor

    Sponsor Paid Advertisement

  4. hj

    hj Moderator & Master Plumber Staff Member

    Aug 31, 2004
    Cave Creek, Arizona
    If you know how to test them and have the equipment, it would be the easiest place to start.
  5. Ford2001

    Ford2001 New Member

    Sep 11, 2009
    property care taker
    Manchester, Vermont
    The breaker may be the cause of your problem. Old breaker, don't handle the inrush current well, check to see if a HACR type should work. Read the motor name plate, and use the
    breaker they call for.
Similar Threads: Electrical Motor
Forum Title Date
Electrical Forum discussion & Blog New basement electrical circuit Sep 27, 2015
Electrical Forum discussion & Blog Boat Dock Electrical Issue Aug 18, 2015
Electrical Forum discussion & Blog New Electrical Service and meter for detached garage Aug 4, 2015
Electrical Forum discussion & Blog Mobile home electrical issue. Jun 30, 2015
Electrical Forum discussion & Blog Electrical code questions. 2005 NEC Jun 15, 2015

Share This Page