    I could not get any 4-2 wg to connect my air handler to my breaker box so I bought 4 copper and 8 copper single strand. Can I bundle these together and run them through the attic like romex or do they have to run in conduit?
     
  2. Jim Port

    Jim Port Electrical Contractor

    Joined:
    Aug 22, 2009
    Occupation:
    Electrical Contractor
    Location:
    Maryland
    Individual conductors like you bought need to be installed in a complete conduit system from the panel to the unit or junction box. You just cannot run conduit part way and slide the conductors through.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. comfun1

    comfun1 New Member

    Joined:
    Dec 11, 2009
    Location:
    S.E. Kansas
    According to my calculations two 4's and an 8 can run in 3/4" conduit and be within the 40% fill rule. Am I right?
     
  5. Jim Port

    Jim Port Electrical Contractor

    Joined:
    Aug 22, 2009
    Occupation:
    Electrical Contractor
    Location:
    Maryland
    What type of conduit?
     
  6. comfun1

    comfun1 New Member

    Joined:
    Dec 11, 2009
    Location:
    S.E. Kansas
    PVC plastic conduit
     
  7. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    My book says 1".
     
  8. comfun1

    comfun1 New Member

    Joined:
    Dec 11, 2009
    Location:
    S.E. Kansas
    There are two 4's and an 8. I looked at a chart and it said 1" for three 4's, so I calculated it for two 4's and an 8 and got 3/4". Was your chart for two 4's and an 8, or three 4's?
     
  9. Jim Port

    Jim Port Electrical Contractor

    Joined:
    Aug 22, 2009
    Occupation:
    Electrical Contractor
    Location:
    Maryland
    Table C9 only allows 1 #4 in a 3/4, and 3 #4s in a 1", based on THHN
     
  10. Alectrician

    Alectrician DIY Senior Member

    Joined:
    Jun 15, 2007
    #4 wire for an air handler?


    Must be heat strips.


    Just get the right cable.
     
  11. comfun1

    comfun1 New Member

    Joined:
    Dec 11, 2009
    Location:
    S.E. Kansas
    You're right. Heat strips it is. I have decided to run them in a 3/4" smurf pipe and see what the inspector says
     
  12. Furd

    Furd Engineer

    Joined:
    Jul 3, 2007
    Occupation:
    Retired energy systems engineer
    Location:
    Wet side of Washington State
    I guess that's okay as long as you don't mind doing it over. One-inch conduit is the correct size.
     
  13. Jim Port

    Jim Port Electrical Contractor

    Joined:
    Aug 22, 2009
    Occupation:
    Electrical Contractor
    Location:
    Maryland
    But those red tags add a splash of color.
     
Similar Threads: need conduit
Forum Title Date
Electrical Forum discussion & Blog Do I need conduit? Aug 3, 2009
Electrical Forum discussion & Blog Does a sub panel in attached space need a main breaker? Friday at 7:19 AM
Electrical Forum discussion & Blog Electrical Circuit Larger Than Needed Feb 1, 2015
Electrical Forum discussion & Blog Need branch ckt diagram for instllation of washer/dryer for permitting Dec 14, 2014
Electrical Forum discussion & Blog Do GFCI Outlets Need a Ground? Nov 14, 2014

Share This Page