Copper pipe reducing the increasing on main waterline

Users who are viewing this thread

Willdabeast

New Member
Messages
2
Reaction score
0
Points
1
Location
Kansas
My customer has a main water line as soon as it comes into the house it is 1 1/2 then reduces to 1/2 in. and then increases the inch-and-a-half again is that a code violation and why do people do that
 

Attachments

  • 20160625_164840_resized.jpg
    20160625_164840_resized.jpg
    106.4 KB · Views: 212

Cool Blue Harley

One Dumb Plumber
Messages
153
Reaction score
31
Points
28
Location
San Francisco, CA
Most certainly a code violation. UPC 610.1 Size Of Potable Water Piping. "...size base on total demand, designed to ensure maximum velocities are not exceeded."

The corrosive resistance of copper pipe is due to an oxide film that naturally forms on the interior walls when in contact with flowing water. If the velocity is too great, impingement, or erosion corrosion occurs, stripping the protective oxide coating and damaging the pipe. Impingement damage occurs when water velocity exceeds eight feet per second in cold water.

There are numerous other code section violations, UPC Table 610.4, building supply, not less than 3/4 of an inch nominal size. "Installation Standards" violations. Too many enforcable violations to list.
 