Thanks for the reply Dana.
Yes, the basement is usually warm.
The apartment is on the second floor. The ductwork runs in the walls of the first floor apartment and above the first floors drop ceiling.
The hot water heater for the apt. is in the basement (30 gal. nat.gas).
Does the 80k unit still seem too big?
Yes, the basement is usually warm.
The apartment is on the second floor. The ductwork runs in the walls of the first floor apartment and above the first floors drop ceiling.
The hot water heater for the apt. is in the basement (30 gal. nat.gas).
Does the 80k unit still seem too big?
I'll bet it keeps the basement warm too, with all of that uninsulated duct work.
I'm assuming that the apartment is 2 or 3 floors up from the basement? (In which case losses from the heating system for the apartment are heating the intervening space.)
Is the hot water heater for the apartment in the basement or in the unit, and is it gas-fired? For heating loads as low as this one likely has it's pretty cheap & easy to heat with baseboards or fan-coils running off the water heater, sealing off the supply & return ducts at the registers. With leaky uninsulated ducted systems like that the duct losses and air-handler-induced infiltration alone could be as high or higher as the actual heat load.
Alternatively, installing a right-sized mini-split heat pump would get you both air conditioning and high-efficiency heating, with comparable (sometimes lower) heating costs to natural gas. With a leaky uninsulated duct system outside of conditioned space it's probably cheaper to operate with a mini-split than the proposed condensing gas furnace. A 1.5-2 ton mini-split is on the order of $4-5K, installed, But if you spent a grand on tighting up and spot-insulating, adding storms to the single-panes, etc. you might get the heat load down to the 1-ton range for a similar installed cost, and even lower operating cost.