Speedy Petey
Licensed Electrical Contractor
MCA of 15A @240V @70'?
12/2 all day. #10 is fine if you want to feel better about yourself. NO REASON AT ALL to go with #8cu.
BTW, the VD calc I use says #14cu is the minimum for 14.7A @240v @70'.
12/2 all day. #10 is fine if you want to feel better about yourself. NO REASON AT ALL to go with #8cu.
BTW, the VD calc I use says #14cu is the minimum for 14.7A @240v @70'.