I'm under IPC. Is connecting a non-bathroom sink (a bar sink) at the location shown in the attached diagram allowable?
 

Attachments

  • NonBathroomSink.png
    NonBathroomSink.png
    25.7 KB · Views: 42

wwhitney

In the Trades
Messages
6,608
Reaction score
1,861
Points
113
Location
Berkeley, CA
Connecting the bar sink at the location shown means the lavatory can't wet vent the shower. But since you are showing a dry vented shower, that's fine. If the shower didn't have its own dry vent, and was depending on the lavatory for its wet vent, then you'd need the bar sink to connect downstream of the shower.