3/4 to 1/2 valve/pipe for shower head

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by tomdiy, Dec 27, 2012.

  1. tomdiy

    tomdiy New Member

    Messages:
    2
    Location:
    nj
    Shower installation with two shower heads each on its own volume valve. The supply into the kohler themostatic valve is 3/4 pex into 3/4 cooper into the valve, exiting the valve is 3/4 copper reduced to 1/2 copper then into each of the 1/2 volume valve and 1/2 copper out to the shower heads, both shower heads seem light on flow both hot and cold (Other fixtures on same feed are fine), Kohler says I should have keep it all 3/4 after the valve but don't most shower heads have to reduce to 1/2 at some point? I was going to replace the valve cartridge to see if it helped but figured I would ask for thoughts before spending the money. Thanks in advance
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,015
    Location:
    New England
    Unless you removed the restrictor (some can be easily, some can't), each shower head is mandated to have a max of 2.5gpm. But, 1/2" pex might be hard pressed to provide 5gpm. The ID of pex is considerably smaller than that of copper in the same 'size' (which is the OD, not the ID). This is because copper is much stronger, so it can be thinner than pex. What's strange to some is that 1/2" copper is unlikely to be 1/2" ID and it is 5/8" OD, although it is much closer to 1/2" than pex.
  3. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,641
    Location:
    Cave Creek, Arizona
    quote; What's strange to some is that 1/2" copper is unlikely to be 1/2" ID and it is 5/8" OD

    The i.d. is determined by the tubing's wall thickness. Type "K" with the thickest wall is ALMOST 1/2" i.d., about 1/40" larger than actual 1/2".
  4. tomdiy

    tomdiy New Member

    Messages:
    2
    Location:
    nj
    Thanks, I guess I was not clear, the flow I am getting is less than I have from predominately 1/2 inch in the other bathrooms, why would 3/4 supply reduced to 1/2 for the last 10 feet of the run after a valve reduce the flow to less than a run which is mostly 1/2 inch
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,015
    Location:
    New England
    Few valves' internal passages are the same diameter as the supply pipes. IF the pipe supplying and outlet of the valve are both the same size, the flow rate increases in the valve and it doesn't act like a restrictor much (the venture effect). If the outlet pipe is smaller, it stays slowed down and the valve is a real restriction to flow. The outlet of a faucet goes through the spout, which is usually unrestricted (well, it may have an aerator on it).
Similar Threads: valve/pipe shower
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Need to move shower drain 0.5 inches Tuesday at 5:17 AM
Plumbing Forum, Professional & DIY Advice, Tips & Handheld shower bar bracket attachment Sep 1, 2014
Plumbing Forum, Professional & DIY Advice, Tips & shower pan liner preslope Aug 30, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Need help identifying shower cartridge Aug 25, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Help me convince my landlord there IS a problem with our shower. Aug 25, 2014

Share This Page