Wiring size for upgraded hot tub

Discussion in 'Electrical Forum discussion & Blog' started by JWR-1, Nov 16, 2007.

  1. JWR-1

    JWR-1 New Member

    Messages:
    1
    I am replacing an existing hot tub with a new one. The new tub requires an electrical service of 240V 60amp. I have upgraded my circuit breakers at the panel and installed a 60 amp GFCI. Currently I am wired using 8awg. Will this wiring be sufficient for a 50' run? Or do I need to upgrade to a #6awg wire?

    Thanks for the help.

    JWR
  2. Bob NH

    Bob NH In the Trades

    Messages:
    3,317
    Location:
    New Hampshire
    Ref: NEC Table 310.16

    8 AWG is rated for 50 Amps if it is not NM or other 60 C wire.

    You need 6 AWG in THWN for outside. You can usually use 8 AWG for the neutral and 10 AWG for the ground unless your inspector gets picky. My last one didn't bother with code and wanted 8 for the ground.

    It will all fit in a 3/4 conduit.