If I have an open 20 amp breaker for my bathroom, can I put the exhaust fan-light combo, a light over the vanity and one outlet together on that circuit?
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
What you propose is fine assuming the fan does not have a heater. The room can and should easily be wired so that the GFCI receptacle does not feed the light/fan unit.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
What you propose is fine assuming the fan does not have a heater. The room can and should easily be wired so that the GFCI receptacle does not feed the light/fan unit.

Then all bets are Off.

It has a heater, A Lightbulb.

Have Fun everyone. Just call me a Smart Ass if you like.

Got to have some Fun.
 
Messages
10
Reaction score
0
Points
1
One circuit supplying a single bathroom would only be legal (codewise) if the home only has one bathroom. It would not have to be wired to the load side of the gfi.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Then all bets are Off.

It has a heater, A Lightbulb.

Have Fun everyone. Just call me a Smart Ass if you like.

Got to have some Fun.
Could not ten baths be wired on ten circuits?
 
Last edited:

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
One circuit supplying a single bathroom would only be legal (codewise) if the home only has one bathroom. It would not have to be wired to the load side of the gfi.
No. Look again. One circuit is only allowed to supply one bathroom if bathroom lights are on the same circuit. One circuit can supply many bathrooms if it hits only the recepts.
 
Messages
10
Reaction score
0
Points
1
No. Look again. One circuit is only allowed to supply one bathroom if bathroom lights are on the same circuit. One circuit can supply many bathrooms if it hits only the recepts.
Well duh.... this one clearly talks of using the fan and heater. .... can you read?
 

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
If I have an open 20 amp breaker for my bathroom, can I put the exhaust fan-light combo, a light over the vanity and one outlet together on that circuit?
Here is the original post.
..... can you read?
I'm not so sure now. The way I read it he wants to put a bathroom on one circuit. That is allowed by code and not restricted to houses only having one bathroom.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
210.11(C)(3) Bathroom Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one 20-ampere branch circuit shall be provided to
supply bathroom receptacle outlet(s). Such circuits shall
have no other outlets.
Exception: Where the 20-ampere circuit supplies a single
bathroom, outlets for other equipment within the same
bathroom shall be permitted to be supplied in accordance
with 210.23(A)(1) and (A)(2).

Maybe he is thinking that the piping is all mixed up and the house needs to be torn down before someone gets killed.
 