Which holes in weatherhead?

Discussion in 'Electrical Forum discussion & Blog' started by Brad in KC, Jul 23, 2008.

  1. Brad in KC

    Brad in KC New Member

    Messages:
    4
    I'm about to install a PVC Weatherhead in preparation for an upgrade to 200 amp service to the house. This two piece service cap has six knockouts. The three closest to the conduit have the advantages of being perfectly sized for the 4/0 4/0 2/0 aluminum entrance conductors and are further back from the lower lip of the 'head, providing greater protection. However, they are so close to the conduit that the wires will need to make a sharp bend.

    On the other hand, the three opening at the outer edge are slots, more than large enough to accomodate the conductors but right in the drip line.

    Does it matter which holes I use?

    Thanks,

    Brad
  2. Speedy Petey

    Speedy Petey Licensed Electrical Contractor

    Messages:
    1,001
    Location:
    NY State, USA
    Nope.
    I use the three slots in a PVC weatherhead.

    The wires should go DOWN out of the weatherhead. This is where your drip loop is most important.