voltage drop
Discussion in 'Electrical Forum discussion & Blog' started by Mike Pastorelli, Jan 22, 2014.
  1. Mike Pastorelli
    Mike Pastorelli New Member
    Jul 12, 2012
    Florida
    My meter point is right at the ( hot ) conductor before the main breaker. The two hots that come off the meter can and into the house before hitting the main panel.. One meter lead is on the neutral and the other on the hot.. Both show 120 volts.. Then, when I turn the microwave on or any large load from any plug everything dims down and on the one conductor the voltage drops to 95 V and the other conductor swings up to 155 Volts.. Cant figure out what is going on? Please advise? Recently purchased forclosure house with what appears to be new service panel.. Thanks :confused:
  2. Reach4
    Reach4 Well-Known Member
    Sep 25, 2013
    Both hots show 120 volts to neutral and you will measure 240 hot-to-hot.
    Are you saying that only two wires come from the "meter can" into the house? That's a big problem that needs fixing.
    Or are you saying that a third wire comes in. Is that third wire at the same potential as your neutral bar? If so, you probably will need to involve the power company. One of the problem may be in the power company wiring. At least one of the problems is in your local wiring. I think you probably want to call your electrician first, but maybe calling the power company first is better. I don't know.
    You have an additional problem in that your local ground connection is not good enough.
    So probably two problems that need fixing. It may be good that you have two problems because one problem alone might have never been noticed.
  4. cacher_chick
    Jan 5, 2008
    Test, Don't Guess!
    The connection to neutral is failing. Make sure yours is tight in the main panel, and if so call the power company. Here, the line from the pole to the meter belongs to the p.c.
  5. DonL
    DonL Jack of all trades Master of one
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    You may have a grounding problem at the Pole Pig, HV transformer.
    The neutral can float if the ground is missing.
    That can be a Big problem.
    Good Luck.
  6. Speedy Petey
    Speedy Petey Licensed Electrical Contractor
    Jun 16, 2007
    NY State, USA
    This is NOT a grounding problem. It is a neutral problem on the secondary side of the utility transformer.
  7. ActionDave
    ActionDave Electrician
    Feb 4, 2009
    Electrician
    Colorado
    Agree with others, bad neutral. Shut off the main and call the power company.
  8. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    OK.
    This old dog loves to learn new tricks.
    Is the Neutral and Ground NORMALLY not the same at the Transformer ?
    They are around here.
    And the Ground at the Meter Service is a safety, just encase there is a neutral fault. It can keep HV from going into the House. Like when a HV transformer shorts out Primary to secondary.
    I understand that it depends on the system used. Some systems carry neutral, some rely on Earth Ground.
    I do like to be corrected if I am wrong.
    Thank You, I want to learn more.
  9. Homeownerinburb
    Homeownerinburb Member
    Jan 14, 2012
    Los Angeles, CA USA
    Just to repeat what you have been told:
    This is a bad neutral from the power company. And it ain't no joke.
    Your whole house could get fried. Have the electric company come out yesterday.
  10. Reach4
    Sep 25, 2013
    You are presuming that the neutral wire was wired into the breaker panel from the meter box.
    We all agree that quick action is required, but the OP seems to be gone.
  11. Mike Pastorelli
    Jul 12, 2012
    Florida
    3 conductors come off the meter can and into the service panel. 2 hots and a neutral. As I said, my DMM reads 118V off each leg with light loads. But, when I plug in larger loads ( microwave or fridge ) the voltage jumps all over the place. I am still looking over this previous owners work ( panel appears to be new - maybe few years old GE goldmark copper conductor bus bars ) Couple observations I can add. I noticed on some romex 12/2 in a crawl space area the wire is chisel damaged a bit, maybe a nick in the neutral. Would a nick in 1 wire cause all this dimming? Also, the meter can and the service panel have separate ground rods that are not connected in a closed loop, but are in contact via the metal conduit pipe that runs from the meter can to the main panel ( through the wall of the house ) I removed the bulb and cleaned and tightened all contacts in the meter can using acetone on a long wood handled small service brush. Please advise? EDIT - Also, forgot to add - I observed a split bolt connector on the neutral leg. I guess the wire was to short and they added 20" of #2 conductor to it. The split bolt connector is very clean and tight and I'm wondering if that could be my issue whereas I vaguely remember people saying this is a no / no. But, if its clean and tight that shouldn't be an issue, correct??? Also, neighbor and I share the same transformer and he says he has no issues with lights flickering or dimming. Problem seems to be mine alone. Thanks Again
  12. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    Where are you measuring the voltage ?
    If you are measuring the voltage at the main breaker, then that would indicate a problem on the service feed.
    You should have the electric company check at the pole or HV transformer.
    They should not charge you for that service.
    Good Luck.
  13. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Instructor
    North Carolina
    No. There is a big difference between the neutral and ground every where on an electrical system
  14. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    As many has already told you call the power company right now.
  15. Reach4
    Sep 25, 2013
    Now you are just trolling. You know that is not true.
  16. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    The neutral is the center tap of a transformer but grounding is the connection to earth in an ungrounded system there will be no neutral from the utility but there will always be an earth connection or grounding if one pleases.
    It is very true that the utility connects their earth ground to the neutral just as we do at the service equipment but the neutral is a current carrying conductor and the grounding is not current carrying a very huge difference.
  17. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    That may be true if JW calls 1 Volt a big difference. But that is about normal, at a outlet on a long wire run drawing 10 amps.
    The difference in ground and neutral, is the Voltage drop on the neutral wire feeding the outlet.
    There should not be a big voltage difference at the breaker panel, If so the feeder wire is to small, or the panel is not bonded properly.
    I doubled with you JW, You did not say "Over" , my mistake, but what you say is true.
    Over
  18. Reach4
    Sep 25, 2013
    Edit: paragraph withdrawn.
    At each house there is normally a ground rod or two that is electrically connected to the incoming neutral conductor. 2. True? 3. Are those ground or neutral rods? In side the first breaker box, the neutral terminal and "ground" terminal strips are connected electrically together inside the breaker box. 4. True? . We understand that is not the case in a sub-panel.
    I know none of those things come as a surprise to you.
    Edit: I just figured out that when you said "big difference" (even on a thread with Voltage in the subject) you meant "big distinction". Green vs white is a difference too, but in the voltage world, I see 2 volts as a difference.
    And jadnashua, care two answer the first 3 questions?
    The Kirchhoff's current law review -- you do have only power 1 wire coming to your neighborhood, right?
    And here is an extra question if you want to respond jadnashua: 5. If there had been a proper grounding/neutralling/wtf system in place at the house, but the neutral wire on the drop was broken, would that symptom the OP saw have been observed? At least 2 flaws here IMO. Power company first. Then maybe more.
  19. jadnashua
    The only time the ground wire/rod should ever carry current is if there is an induced voltage as from a lightning strike or a fault in the system...IOW, the ground lead should NEVER have current running through it except in exceptional circumstances. Power needs a complete circuit and that's from the hot lead to either the other side of the transformer directly (in a typical 240vac residential system), or via the neutral lead, which still gets to the other side of the transformer, but not passing through ground.
  20. bluebinky
    bluebinky Member
    Aug 31, 2011
    Software Engineer
    Santa Clara, CA
    I agree with JW on this one. Also, agree about shutting off the main breaker until the problem is fixed.
    I have a silly question. Are there any main breaker panels that can be configured as a sub-panel -- by removing a bonding screw?
  21. Reach4
    Sep 25, 2013
    It looks like I was wrong about the distribution transformer grounds; it seems they have separate ground rods and wires for the high and low voltage sides. I wonder if it has been like that forever or if that practice started after sharing grounds for years. Anyway, here is the schematic using separate grounding rods: [​IMG] I still think the OP's system has at least two problems.
Similar Threads: voltage drop
Electrical Forum discussion & Blog Strange Voltage Drop When Light Bulb is Installed Aug 8, 2015
Electrical Forum discussion & Blog Voltage drop in underground cable May 16, 2012
Electrical Forum discussion & Blog Service entrance cable size & voltage drop Aug 21, 2009
Electrical Forum discussion & Blog Lights flicker and Voltage Drop Question Dec 16, 2008
Electrical Forum discussion & Blog Activating Pump via low voltage switch input Feb 11, 2017