triangle tube prestige 110

Discussion in 'Boiler Forum' started by mark161, Oct 17, 2012.

  1. mark161

    mark161 New Member

    Messages:
    1
    Location:
    ma.
    looking for wiring info using a taco SR 503 switching relay with a prestige 110 boiler
  2. zl700

    zl700 DIY Senior Member

    Messages:
    237
    Location:
    Texas
    Taco XX terminals is wired low voltage 18-2 wire to prestige TT terminals
    Last edited: Oct 17, 2012
  3. TerryP

    TerryP New Member

    Messages:
    1
    Location:
    Toronto
    My TT boiler is cycling but it is skipping the space heating mode (3) and only heating the domestic hot water. The domestic mode (4) heats to as high as 204, according to the display, then shuts down having reached the temperature set point. The display then flashes 6200, followed by code b 18 (supply temperature too high). Am I not getting space heating because the supply temperature is too high?
  4. BadgerBoilerMN

    BadgerBoilerMN Master Hot Water Mpls,MN

    Messages:
    303
    Location:
    Minneapolis
    If the TT is set for domestic hot water and unable to satisfy this first priority, it will not leave the task. Who set the boiler up?
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,817
    Location:
    New England
    It could be as simple as the temperature sensor for the IWH is not seated properly, or not working properly. Is the IWH temperature excessive?
  6. Machinist

    Machinist New Member

    Messages:
    5
    Location:
    Ithaca, NY
    Terry,
    What was causing the issue with your TT skipping space heating mode? Is it a Prestige 110 that has been in service a while? A followup might be helpful for others.