Tie sink vent & boiler vent together?

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by zaothusia, Jan 4, 2010.

  1. zaothusia

    zaothusia New Member

    Messages:
    5
    Location:
    Minneapolis MN
    I have a wall mounted high efficiency boiler. It is direct vented with 3 inch PVC outside the house. I am going to be adding a sink and need to vent it quickly, can I tie into this, or will it cause my boiler to run less efficient?

    If I cannot tie into this I am wonder if anyone knows if an AAV is legal in Minneapolis, Minnesota? I would prefer to not have to redo this in the future:)
  2. krow

    krow Plumber

    Messages:
    906
    Location:
    Ontario, Canada
    Don't you dare try that. You could end up killing yourself if any methane gas gets in the boiler while its firing, if you don't blow up the neighbourhood first

    I'm not sure if AVV's are legal in Minneapolis, but it would be better than the original idea.
  3. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Messages:
    810
    Location:
    Penticton, BC
    no..................
  4. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Got to be the best post of the year :D
  5. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    27,237
    Location:
    Cave Creek, Arizona
    vents

    That would not be the best idea you have had this year, nor the smartest one. I can just imagine someone doing that, and then using AAV's on all the other drains and wondering why NOTHING drains properly while the boiler is operating.
  6. Daltex

    Daltex New Member

    Messages:
    15
    Location:
    Texas
    I know you wouldn't have posted this if you understood the implications of doing it. Quick answer is for a quick vent use an AAV if only for the one sink. May not be code so you might want to check it out with the city first. They are not quiet btw.

    Problems with connecting the vent to the boiler vent=

    When the boiler fires, it will have positive pressure running in the vent. This could/would cause the exhaust along with the CO and combustion by products to push its way through the sink's p-trap and cause deadly gas to be released inside your home.

    The vent from the sink will be connected to the main sewer line which has methane gas and odors. When the blower is in between cycles, the methane could be vented back inside your boiler. When ignition occurs- bang! There is no p-trap on the exhaust vent so it could also fill the room with methane along with the sewer odor.
    Last edited: Jan 5, 2010
  7. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Messages:
    810
    Location:
    Penticton, BC
    What deadly gases? A properly burning gas appliance doesn't produce any deadly gases. You could obviously produce carbon monoxide but it's not a regular byproduct of combustion in anything close to deadly amounts. But don't get me wrong I'm certainly not trying to say this guy should hook up his plumbing vent to his gas vent.


    You know that natural gas and propane (the stuff being burned in the boilers) are just forms of hydrocarbons so is methane (in fact NG is basically methane).

    Not only that all boilers that are electronically ignited have a prepurge time of the fan to clear the combustion chamber of any gases.

    And on top of that you need the proper mixture of air to methane to combust it. So is it possible that you could ignite methane from the sewer inside the combustion chamber and have it explode all the way back into the city sewer..... absolutely not.
  8. frenchie

    frenchie Jack of all trades


    http://www3.gendisasters.com/idaho/14377/sand-point-id-sewer-gas-explosion-may-1916

    http://query.nytimes.com/gst/abstract.html?res=9506E5D91231E033A25756C2A9649D94659ED7CF

    http://query.nytimes.com/gst/abstract.html?res=9907E0D8103DE433A25751C0A96E9C94649ED7CF

    http://news.google.com/newspapers?n...ecNAAAAIBAJ&sjid=nm0DAAAAIBAJ&pg=3887,1484502

    http://news.google.com/newspapers?n...ecNAAAAIBAJ&sjid=nm0DAAAAIBAJ&pg=5847,1487983

    http://www.wreg.com/news/archive/holly-springs-house-explosino,0,4337430.story
  9. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Messages:
    810
    Location:
    Penticton, BC
    Only the last article is from post 1930 and it doesn't even say conclusively that it was sewer gas that caused the explosion in the house. They just had no other explanation so they picked sewer gas as the culprit. Certainly not rock hard evidence.

    All the other articles (glanced over them quickly) were caused from someone actually down inside the main sewer with an open flame or another source of ignition like a short in some underground wiring. Again they were all basically from 80+ years ago too.

    So I don't think any of those articles prove what I said is wrong. I'm not saying sewer gas can't be explosive but the chances of a HE boiler with a positive vent pressure lighting up your neighbourhood's sewer is 0%.
Similar Threads: sink vent
Forum Title Date
Plumbing Forum, Professional & DIY Advice Adding garage utility sink - use existing 1st floor bathroom drain and vent? Nov 13, 2014
Plumbing Forum, Professional & DIY Advice Gurgling after using bathroom sinks - venting question! (pic attached) Aug 19, 2014
Plumbing Forum, Professional & DIY Advice Need advice on vents for sink and tub Aug 3, 2014
Plumbing Forum, Professional & DIY Advice wet vent tub and sink - will this work? May 7, 2014
Plumbing Forum, Professional & DIY Advice Draining sink into vent pipe Apr 19, 2014

Share This Page