The poll -- Phasing of Voltages out of a Transformer

Discussion in 'Electrical Forum discussion & Blog' started by Reach4, Feb 26, 2014.

?

Please select the best answer from these choices:

Poll closed Tuesday at 1:27 PM.
  1. Voltage A is in phase with voltage B.

    50.0%
  2. Voltage A is out of phase with voltage B. (180 degrees out of phase)

    33.3%
  3. It is meaningless to try to say whether those voltages are in phase or not.

    16.7%
  4. No AC voltages powered by single core transformer are out of phase.

    0 vote(s)
    0.0%
  1. Reach4

    Reach4 Well-Known Member

    Messages:
    2,837
    Location:
    IL
    huge2.png

    T1's primary is powered by 4000 VAC 60 Hz single phase power. The secondary of the transformer has 240 VAC between point A and point B. The transformer is shown with two secondary windings, but this is equivalent to a single center-tapped secondary in this case.

    The voltage at GND, is our reference. Assume ideal circuits.
    Last edited: Feb 26, 2014
  2. jwelectric

    jwelectric Electrical Contractor/Instructor

    Messages:
    2,569
    Location:
    North Carolina
    Being that the secondary as pictured is a single phase 240 volt winding there is no way that anything in that picture can be out of phase except for the primary to the secondary. As the picture shows at 1 on the primary is a dot and on the secondary the dot is 180 degrees displaced and is found at 7 and 5.

    I order for the two 120 volt windings to be 180 degrees displaced then the dots would be at opposite ends or in the center together.

    Considering one quarter of a football game where one team is trying to take the ball to one goal and the other team is trying to get the ball to the other goal both teams are running at 180 degrees against or out of phase if you please.

    In a single winding or even the two windings you have posted the current will flow through the winding from one end to the other end and the laws of physics will not allow those electrons to oppose each other by being 180 degrees out of phase.

    If you cannot grasp that what you are seeing on the scope is both ends of the sine wave looking toward the middle then there is not much hope of you ever making anything but a helper. Being able to figure the arc flash abilities of a panel would be totally out of the question.

    Take a three phase 240 volt delta transformer and tap the center of one winding. From the corner of the tapped winding to the tap will be 120 volts. From the center tap to the odd winding will be the square root of the voltage from the center tap to the odd winding squared minus the square of the voltage from the center tap to the end of the winding that is tapped. 240 times 240 equals 57600. 120 times 120 equals 14400. 57600 minus 14400 equals 43200. The square root of 43200 equals 207.84.
    A short cut one can take is to multiply the 120 by the square root of three which will be guess what, yep 207.84

    Should we use this 240 volt three phase to power a 10 kw heater the amperage draw would be 24 amps. How one might ask. Multiply 240 by the square root of three to get the three phase voltage of 415.

    I have been teaching electrical theory for a decade and a half, a lot more time than it takes to get a PHD.
  3. Rich B

    Rich B DIY Senior Member

    Messages:
    283
    Location:
    New Jersey
    I voted with JW before I read his post.....The secondary side is all in phase...
  4. jwelectric

    jwelectric Electrical Contractor/Instructor

    Messages:
    2,569
    Location:
    North Carolina
    Exactly but the entire secondary if 180 degrees out with the primary
    in the diagram above there are two windings but they are connected just like it was one. As drawn it is like a broken magnet, two magnets that attract each other. If they were 180 degrees out with each other then the like poles would repel and all electron flow would stop. As the magnetic fields built up the two opposing fields would cancel each other out and there would be no electron flow.
  5. Rich B

    Rich B DIY Senior Member

    Messages:
    283
    Location:
    New Jersey
    JW I have no formal electrical training...just years of working on machines and trying to understand. I fix welders and generators. Some very complex stuff today. Makes my head spin and hurt but I learned to read prints and how to components on my own...
  6. DonL

    DonL Jack of all trades Master of one

    Messages:
    4,528
    Location:
    Houston, TX

    There is something wrong with that picture.

    How can all of the current be flowing in the same direction ?


    Carry on.
  7. Reach4

    Reach4 Well-Known Member

    Messages:
    2,837
    Location:
    IL
    It's AC. It's algebraic/vector math.
    http://en.wikipedia.org/wiki/Kirchhoff's_circuit_laws
    Those arrows are drawn fitting the sum of currents in a network of conductors meeting at a point is zero. If one of the arrows is drawn the other way, the phase will differ by 180 degrees, and we would use the other form of KCL.
  8. DonL

    DonL Jack of all trades Master of one

    Messages:
    4,528
    Location:
    Houston, TX
    Sounds like Jerkoff's law to me.

    If you do not have a return current path, then you do not have any transformation of power. Your Transformer is bad.


    Have fun.
  9. BobL43

    BobL43 DIY Senior Member

    Messages:
    1,799
    Location:
    Long Island, NY
    The way I see it, I agree with our moderator, and I think that Current path C is null as the current will all flow from A to B throught the equall resistive loads. then again, as Don said, Jerkoff's law applies here. We all seem to not have the Capacity or have Relcutance to seeing this clearly and are Impeding the resolution of this issue. As the Borg said; Resistance is Futile.:p;)

    http://www.youtube.com/watch?v=AyenRCJ_4Ww
    Last edited: Feb 27, 2014
  10. DonL

    DonL Jack of all trades Master of one

    Messages:
    4,528
    Location:
    Houston, TX
    I think I figured out why that transformer has no current flowing.

    Them 10 Watt resistors opened. lol

    I have never seen a transformer that has a Exact 180 degree phase shift, Even from primary to secondary.

    Even a vacuum can not make that transformer so precise. A degree or three off maybe.


    Have Fun Everyone.
    Last edited: Feb 27, 2014
  11. Reach4

    Reach4 Well-Known Member

    Messages:
    2,837
    Location:
    IL
    Assume ideal circuits.
  12. Reach4

    Reach4 Well-Known Member

    Messages:
    2,837
    Location:
    IL
    Delete... duplicate post.
  13. DonL

    DonL Jack of all trades Master of one

    Messages:
    4,528
    Location:
    Houston, TX

    A ideal circuit would be to get rid of the transformer, and feed the load directly.

    Any conversion is a loss of power.


    Is it not ?
  14. Rich B

    Rich B DIY Senior Member

    Messages:
    283
    Location:
    New Jersey
    I was thinking of the circuit as being open ended and the resistors were there to represent 2 separate 120 volt loads.......

    A 4 wire generators output is wired like this, well sort of but not exactly...........minus the resistors and there is no transformer....add a rotor to where the primary side is........

    I work on them all the time.......Onan RV units......
    Last edited: Feb 27, 2014
  15. ankhseeker

    ankhseeker Member

    Messages:
    80
    Location:
    California
    Are you saying that you suffer from hysteresis?
  16. DonL

    DonL Jack of all trades Master of one

    Messages:
    4,528
    Location:
    Houston, TX

    Yes, I guess you could say that.

    And Rotten to the Core.


    Electricity needs good relationships to play nice.
  17. jwelectric

    jwelectric Electrical Contractor/Instructor

    Messages:
    2,569
    Location:
    North Carolina
    just what is your background in the electrical field? Current is the flow of electrons. I will not debate the conventional or electron flow but it flows from negative to positive and cannot flow in opposing directions such as in the diagram you have posted.
    Last edited: Feb 27, 2014
  18. DonL

    DonL Jack of all trades Master of one

    Messages:
    4,528
    Location:
    Houston, TX

    Well, I did not see a answer.

    So I guess it is time to do some schooling.

    http://en.wikipedia.org/wiki/Leading_and_lagging_current

    http://en.wikipedia.org/wiki/Alternating_current

    That may take some time to sink in.


    Have Fun Everyone.
  19. BobL43

    BobL43 DIY Senior Member

    Messages:
    1,799
    Location:
    Long Island, NY
  20. houptee

    houptee Member

    Messages:
    186
    Location:
    Monmouth County, NJ
    In the USA we use this type of distribution system.

    http://en.wikipedia.org/wiki/Split-phase_electric_power

    A split-phase electricity distribution system is a three-wire single-phase distribution system. It is the AC equivalent of the original Edison three-wire direct current system. Its primary advantage is that it saves conductor material over a single-ended single-phase system while only requiring single phase on the supply side of the distribution transformer.[1] The two halves are 180 degrees apart with respect to center point. It may also be called three-wire, single-phase, midpoint neutral system.