Testing new residential waste/ vent system?

Users who are viewing this thread

Ian Lockwood

New Member
Messages
4
Reaction score
2
Points
3
Location
California
Hi all,



I've replaced the entire waste system in my home and currently have the new system plugged at the city's connection and full of water to the top of the lowest vent coming out of the roof in order to test for leaks. I'm losing 1"-2"/day of head in the vent stacks, but can find no leaks in any of the in wall connections. I preformed the same test for just the underground portion of the system before burying it and lost no head over the same time period. I've gone around and burped all the air that I can out of trap arms and cleanout risers and am still losing about the same amount of head over a day's time. It's been hot, in the 90's, where I live during the day, but this seems like more than I should lose to evaporation. Can anyone offer advice?



Thanks,
Ian
 

Cacher_Chick

Test, Don't Guess!
Messages
5,461
Reaction score
214
Points
63
Location
Land of Cheese
Install a test fitting at the point where the building drain exits the structure and use a test ball to divide the inside piping from the outside. Detetmine if if the inside passes the test. The standard is 10' of head pressure. You can use test fittings and best balls to isolate seperate branches of the system until the leak is found. This testing is nomally done before any traps are installed. If you cover the top of the vent, there should be almost no evaporative loss.
 