Support for cast iron vent

Users who are viewing this thread

Jetboy55

Member
Messages
85
Reaction score
4
Points
8
Location
Wisconsin
I am replacing my cast iron. The 3in cast iron goes thru roof boot. I was gonna pull it out also, but I've become concerned the boot won't fit the pvc replacement pipe properly since they have different od's. Can I cut the cast iron a little below the roof and just leave it? If so, what coupling to make the transition and do u need to support the remaining cast iron since it will only be a few feet long? Thanks all.
 

Breplum

Licensed plumbing contractor
Messages
2,009
Reaction score
829
Points
113
Location
San Francisco Bay Area
There are specialty transition ftgs for all types of piping.
Mission makes one CP33. Only use a full shielded stainless steel band and not just rubber with two hose clamps.
If your stack is straight up, then 2 ft of CI poissibly ok.
It is ideal when the stack is straight to use a 'riser clamp' at the ceiling joist below. They make short eared ones too.