Spa GFI Location
Discussion in 'Electrical Forum discussion & Blog' started by pimel@wildblue.net, May 22, 2008.
  1. pimel@wildblue.net
    pimel@wildblue.net New Member
    May 21, 2008
    I am new to the forums. I ran 2+ground wire cable to my spa panel location(45 feet) since the spa I was getting has a two+ground requirement. The GFI has a netural and I am told that eventhough I have grounded the spa panel with a grounding rod I cannot ground the nutral at the spa sub panel.
    My QUESTION: Can I install the GFI breaker at the source of the spa cable(sub panel in the basement) that has a nutral bar connected and place a regular breaker in the spa panel which is 6' from the spa location? Both spa and panel are on an exterior deck.
    Mel C
  2. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Instructor
    North Carolina
    680.42(C) will allow the equipment grounding conductor to be un- insulated for that portion that is on the interior of a building for a single family dwelling but the conductors you mention are not supplying the motor and are feeding a remote panel instead making 680.42(C) viod.
    This tub is being installed outside.
    These conductors will be feeders and must comply with
    As for the ground rods I am at a loss as they are not needed if this tub is
    and the deck is attached to the house.
    Install the feeders and isolate the grounded (neutral) at the remote panel. Bond the insluated equipment grounding conductor to the enclosure for the remote panel and the equipment grounding conductor of the tub.
    With this type of installation the GFCI can be installed at the remote panel. Keep in mind that you are mixing treated water and electricity in the same area that you plan on playing so safety should be in the upper most concern. Making it work is not the answer that you are looking for right now as just because it works does not mean that it is safe.
    This tub will also be required to adhere to 680.22(A)(3) also. A receptacle no closer than 10 feet and no farther away than 20 feet will need to be installed. By moving the remote panel away from the tub and installing four conductors the receptacle can be located in the same area and be fed from the same panel.
  4. Speedy Petey
    Speedy Petey Licensed Electrical Contractor
    Jun 16, 2007
    NY State, USA
    All the information Mike gave you is correct and necessary.
    The quick answer to this question is YES.
    I just have to ask, WHO (incorrectly) told you you needed a ground rod at the tub????
    That rod is NOT "grounding" anything...at all, and is basically useless in this application.
  5. pimel@wildblue.net
    May 21, 2008
    Clarification
    I guess I wasn't too clear and maybe confused the issue with too much information. First of all the GFI breaker has a neutral (white) . The Cable from the house panel to the spa panel only has the two supply and a ground, no white neutral. So I proposed to place the spa (50 Amp) GFI in the house panel so I could attach the GFI nutral to the panel's neutral bar. And place the standard 50amp breaker in the disconnect box in the proximaty of the spa(6' in view). So the question was does it matter which end of the supply lines to the spa panel the GFI is located?
    The grounding bar was present for grounding of the satelite system and I believed grounding the spa panel would be an additional safty measure to the insulated ground wire from the disconnect to the supply panel. No one advised it was required for the spa but it is adajacent to the panel and deck and handy.
  6. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    See answer by clicking here
Similar Threads: Location
Electrical Forum discussion & Blog Subpanel location, mounting on the joist Jan 31, 2014
Electrical Forum discussion & Blog 3-way switching, outside damp location, off of a GFCI Dec 5, 2013
Electrical Forum discussion & Blog GFCI's at all outlet locations Aug 17, 2011
Electrical Forum discussion & Blog Subpanel location question Jun 5, 2011
Electrical Forum discussion & Blog Code question on multi-location dimmers ( lutron / maestro ) Dec 28, 2009