Running ducted air handler condensate lines to sewer ejector pit against code?

Users who are viewing this thread

Aberrant

New Member
Messages
11
Reaction score
0
Points
1
Location
Boston
I have 2 ducted Mitsubishi air handlers in my basement that are within 3 feet of my sewer ejector pit that serves my basement full bathroom. Is it against code to run the condensate drain lines for these air handlers to the ejector pit? I'm located in Massachusetts if that matters.
 

Breplum

Licensed plumbing contractor
Messages
1,966
Reaction score
798
Points
113
Location
San Francisco Bay Area
Never directly, only via a gapped drain fitting. Often a 2" properly vented p-trapped standpipe with a inverted 3 x 2 bell increaser to make the receptor diameter bigger.
 