    I have a closed hydronic boiler system with a spirovent/extrol attachment. I've been having a problem with the spirovent.

    Whenever my circ pumps turn off, water shoots out of the relief valve on top of the spirovent for a couple of seconds in a solid stream. I lose so much water that every couple of months I have to add more water so to maintain pressure.

    Here are my questions: why am I losing so much water through the spirovent, and what can I do about it?

    Thanks again,

    Chuck
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,892
    Location:
    New England
    From what I read, they have a lifetime warranty. I checked with them awhile ago, and they said if you remove the top half (a strap wrench should work), you can soak that part in vinegar for a few hours and it should clean it up and restore it. Might be a pain to do while in the heating season. Give them a call or drop them an e-mail...they seemed pretty responsive ad there may be some more info on their website. I think the working parts are limed up, and cleaning it should restore it. If not, then I don't know.
  3. patrick88

    patrick88 Plumber

    Messages:
    836
    Location:
    Webster Ma.
    Last I checked It's a 10yr warranty. If the system is not refilling its self You should replace the feed also. It should keep the system at a constant pressure.
  4. chuckthenovice

    chuckthenovice New Member

    Messages:
    2
    Spirotherm had the answer

    Thanks for the info/advice. I contacted Spirotherm as recommended by this forum. They had the answer (see below for their actual response). Turns out that the problem wasn't lime build-up but that my expansion tank sat on the wrong side of my circ pump.

    -Chuck


    Thank you for your e-mail. Usually when this happens the expansion tank is in the wrong location and the temporary pressure imbalance when the pump turns off causes the head to flood and the stream of water. If the head needed cleaned the Spirovent would drip and have no bearing on what the pump is doing. Proper location of expansion tanks is always on the suction (inlet) side of the circ pump. In other words, always pump "away" from the tank, not towards it. The reason has to do maintaining design pressure in the system and is difficult to explain in an e-mail. Check your tank connection and if it is after the pump, consider putting a "T" in the line before the pump and connecting it there. That should solve the problem. If not, let us know and we will try to assist further.


    Spirotherm, Inc.
Similar Threads: Problem Spirovent
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & new house, only galvanized pipe left = problems. Aug 9, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Have a problem pipe in my barn not sure how to fix advice please? Aug 4, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Fridge Water Line Problem Aug 1, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Not fully seated PVC toilet waste lines problem??? Jul 23, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Water softener installation problem Jul 18, 2014

Share This Page