    I have a gas boiler with steam radiators. My boiler pressure keeps going up to 5 psi and the pressure relief valve opens. I adjusted the pressuretrol (0.5 psi with differential 2 psi) but cannot solve the problem. The burners seem to stay on even though the pressure in the boiler has passed the cut out setting. I am wondering whether this happens due to pressure relief valve, pressuretrol, or other sensing components. Recently some erosions in returning pipes have been fixed by breaking a joint and replacing smaller size pipe (from 2 inches to 1 1/4 inches) in some part.

    Thanks.
  2. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    The pipe and or inlet to the pressure-trol is plugged up with crap.

    If that isn't the problem then the pressure-trol itself is bad (though very rarely) or someone has screwed up the wiring because regardless of thermostat and or aquastat settings the pressure-trol is the main operating limit for a steam boiler. Thank god the pressure relief valve is working because if it had failed to open you are looking at a catastrophic explosion.
Similar Threads: pressure relief
Forum Title Date
HVAC Heating & Cooling Calculation for max primary hydronic pump gpm/pressure Sep 29, 2014
HVAC Heating & Cooling vacuum vs non-vacuum valves in a 1 pipe low pressure steam heating system ? Jan 16, 2012
HVAC Heating & Cooling Setting pressure in hot water boiler Dec 12, 2011
HVAC Heating & Cooling Both suction & discharge pressure drops into vacuum when unit runs. May 18, 2011
HVAC Heating & Cooling Boiler water pressure too high ... Feb 8, 2011

Share This Page