pilot goes out with new thermocouple

Discussion in 'Water Heater Forum, Tanks' started by ilya, Feb 25, 2011.

  1. ilya

    ilya In the Trades

    Joined:
    Dec 10, 2009
    Occupation:
    home repair -I am not licensed and never represent
    Location:
    Akron Ohio
    A gal I've done a little work for has a 7 yr old Richmond water heater. I've replaced the thermocouple but the pilot still goes out after a few hours. Any deas would be appreciated.
     
  2. Cookie

    Cookie .

    Joined:
    Oct 7, 2005
    Location:
    .
    You need a new gas control valve.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    There can be more than one cause of the pilot going out, and the only way to determine which is the cause would be to watch it in operation. In many cases, if you replace the control valve, you still have the problem. And, I would replace the heater before I would spend time and money on a new gas valve.
     
  5. DonL

    DonL Jack of all trades Master of one

    Joined:
    Mar 30, 2011
    Occupation:
    Rocket Scientist
    Location:
    Houston, TX
    I agree with hj.

    Also make sure the thermocouple is positioned in the flame properly. And that there is no draft causing the pilot flame to go out.

    Have a great day.

    DonL
     
Similar Threads: pilot goes
Forum Title Date
Water Heater Forum, Tanks Pilot Light goes out intermittenly Oct 1, 2014
Water Heater Forum, Tanks New Install AO Smith XCV-50 Pilot Light Issue Jan 31, 2015
Water Heater Forum, Tanks water heater pilot light won't stay on May 7, 2014
Water Heater Forum, Tanks Pilot Light Stays Lit Yet Hot Water Does Not Come On Dec 4, 2012
Water Heater Forum, Tanks "State" Gas Water Heater- Pilot won't stay lit - replaced thermocouple Aug 20, 2012

Share This Page