No heat on second floor
Ennismj
I have a forced hot water system and I can't get any water to the second floor. I opened the bleeder valves on the base boards and a little air comes out but not much. My pressure is set at 22 and from the basement to the 2nd floor the distance is about 19'. I followed the supply pipe and noted where the branch goes to the second floor. About 2' from where the branch comes off the supply, the pipe is hot then there is a drain valve and shortly after the pipe is not hot and likely waterless. I have tried combinations of shutting the boiler off, shutting the water supply off, draining but still can't get water/heat to the 2nd floor. Thoughts?
Rmelo99
Network Engineer
Some questions, is this one zone or multiple?
If it is multiple zones are there multiple circulator pumps or zone valves?
Any leaks anywhere? If so you may need to add some make up water. Is there an auto-fill valve and if so is the water feed valve open or closed?
Usually you need to push water up the supply side and purge at the return.
Come back to us with more info and pics if possible so we can better help.
Are you saying if you open the bleeder valves, if you leave them open, you never get any water out of them?
Is there a zone valve that isn't opening? They can often be manually opened with a bypass lever.
Doherty Plumbing
Journeyman & Gas Fitter
Penticton, BC
www.facebook.com
The height of a closed loop system is irrelevant....
Just a thought but you may want to reduce the pressure from 22 to about 17psi....
Sounds like a standard air lock to me! You should bleed the bleeder for a WHILE into a bucket or something (I use a 1 gal. shop vac). You may get some water with a bit of air but there could be a big air bubble behind all of that air/water.
Bleed each bleeder WHILE the system is hot until you get hot water coming out of the bleeder. If you do this and then still have problems you have other issues!
Let me know how it goes!
Ennismj
Update
Yes, only one zone, one circulator, one thermostat.
The make up water supply is open and presumably filling the system.
Still no luck getting water to the second floor...just a little air...then nothing.
heat
You may be violating one simple rule of physics. If the pressure is actually set at 22' OR 22psi, and the radiation is only 17' above the gauge, AND you do not get water out of the system when you open the bleed valve, then you have found a way to increase gravity INSIDE the system so the water cannot rise to the level of the bleed valves. Either that or you have a bad gauge and the pressure is actually less than you think. I am in favor of the latter cause.
NHmaster
S. Maine
I would change the gauge for sure, but I'll bet a whole lot that there is air in the system and getting it out can be a pain. Every system is different. Sometimes there are air bleeders on the radiation or the high point in the piping, other times the system gets purged at or near the boiler or hell, I have even seen purge valves many feet away from the boiler especially if the loop is split. That's what makes explaining how to purge a system so hard to do without being there. I think that the best thing to do at this point is call a heating Tech that knows what he's doing. It shouln't take him more than an hour to purge it out.
Ennismj
Problem Solved
It appears the pressure reducing valve on the make-up water line was not functioning...it was stuck. Anyway, a cleaning of the screen and flip of the lever enabled the system to fill. Everything is operational. Thanks for the reply's and ideas.