    Will there be any problems with the photo below.
    On the right is a 2in line that is connected to a floor drain on the other side of the wall. This follows onto the main stack which is 4 feet away.
    I have the p-trap for the new shower that is connected to the wye that follows on to connect to th 2in line from the floor drain to the main stack. Connected via fernco.
    On the left is the vent for the shower that will lead up the wall and is vented via an AAV

    Attached Files:

  2. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    27,247
    Location:
    Cave Creek, Arizona
    Yes, your horizontal vent is not above the flow line of the drain, and not 6" above the overflow level of the shower, and not at least 42" above the floor, all of which are requirements for a horizontal vent line.
  3. skier884

    skier884 New Member

    Messages:
    4
    Location:
    nebraska
    If i bring the vent pipe up to at least 42" then run it horizontally I should be OK then?
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,313
    Location:
    New England
    Also note that the AAV, if allowed in your jurisdiction, must remain accessable...it can't be behind a wall unless there is an access panel. It must remain available for service as they do fail eventually.
  5. skier884

    skier884 New Member

    Messages:
    4
    Location:
    nebraska
    My other question would be do I even need a vent since I am so close to the main stack, with only the floor drain on the line with the shower. One issue might be that the laundry drains into the floor drain.
  6. cacher_chick

    cacher_chick Test, Don't Guess!

    Messages:
    3,274
    Location:
    Land of Cheese
    I don't know of anywhere that allows the laundry to drain into a floor drain.
    Without a vent the discharge from the laundry will siphon the shower trap.

    The vent line cannot run horizontally until it is at least 42" above the floor.
    You have it running horizontally below the floor.
  7. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    27,247
    Location:
    Cave Creek, Arizona
    quote: If i bring the vent pipe up to at least 42" then run it horizontally I should be OK then?

    Yes, but how will you get rid of the horizontal pipe out of the "Y" and bring it up vertically?
  8. skier884

    skier884 New Member

    Messages:
    4
    Location:
    nebraska
    If i twist the Y so it has the vent line above the drain line would that correct the problem? If not do you have any suggestions of what would i should do? Thanks for all your help
    Last edited: Mar 6, 2010
Similar Threads: basement bathroom
Forum Title Date
Plumbing Forum, Professional & DIY Advice Basement Bathroom Toilet Flush Issues Yesterday at 6:50 AM
Plumbing Forum, Professional & DIY Advice Basement bathroom install - cleanout? Oct 21, 2014
Plumbing Forum, Professional & DIY Advice Basement Bathroom with Ejector - Is existing plumbing to code? Oct 10, 2014
Plumbing Forum, Professional & DIY Advice How to best ballpark price for a new basement bathroom? Jul 28, 2014
Plumbing Forum, Professional & DIY Advice Vent issue new basement bathroom Jul 23, 2014

Share This Page