navien ch240 hot water takes a while to reach fixtures

Discussion in 'Tankless Water Heater Forum' started by Sparkymurph, Oct 2, 2011.

  1. Sparkymurph

    Sparkymurph New Member

    Joined:
    Oct 2, 2011
    Location:
    Virginia
    With a new installation of a Navien ch240 combi boiler/hot water unit, the hot water takes a good 45 seconds to reach a fixture that is only 3 feet from the unit. The manual says to take the circulating pump off of freeze protection mode. I cannot find any procedure on how to do go about changing the mode. There is nothing in either manual or online. Any ideas?
     
  2. zl700

    zl700 DIY Senior Member

    Joined:
    Aug 26, 2009
    Location:
    Western NY
    Changeover time from a cold start is only 15 seconds so your wait should only be 20 seconds tops leading me to believe something is wrong with piping or install.
    Go to orange manual and with Navien remote installed, try programming the DHW preheat option so that hot water should leave heater instantly. You can always call the 800 number on back of manual for assistance.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Surfing Plumber

    Surfing Plumber New Member

    Joined:
    Sep 27, 2011
    Location:
    Orange County, CA
    I installed a good amount of Navien in my career, all i gotta say is I got call backs on 80% of them. There always something wrong with them, if not the switch sensor, or is the circuit board. The built-in recirculation system doesn't even work well.. it is just a selling gimick..I say to stay away from Navien. You get what you pay for...
     
  5. zl700

    zl700 DIY Senior Member

    Joined:
    Aug 26, 2009
    Location:
    Western NY
    Surfer, do you read installation manuals as well as posts? No wonder you have problems, it's about the combi not a Tankless, there is no recirc on a combi.
     
Similar Threads: navien ch240
Forum Title Date
Tankless Water Heater Forum newbie on navien ch 240 Mar 2, 2017
Tankless Water Heater Forum Cost of install for Navien NPE-210A Feb 28, 2017
Tankless Water Heater Forum Navien NPE horizontal venting pitch? Jan 30, 2017
Tankless Water Heater Forum Controling Navien NPE internal recirculation pump Dec 15, 2016
Tankless Water Heater Forum Navien cr-240A water heater problem Nov 15, 2016

Share This Page