Minimum Trap Arm Length

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by handyman923, May 30, 2013.

  1. handyman923

    handyman923 New Member

    Joined:
    Nov 20, 2006
    Location:
    Portland, OR
    Is there a minimum trap arm length for a washer stand pipe? Right now, I have the outlet from the P-trap butting tight to the sanitary tee. Is this too close? Will this create a S trap?

    Thanks for any advice!
     
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    I think I read two pipe diameters, but don't quote me on this...
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    trap

    Depending on how you measure the trap arm, the two fittings may "force" it to be at least two diameters between the "pipes". IF you have a proper vent you cannot "create" an "S" trap as long as the maximum length is within the parameters for the pipe size.
     
  5. denikar

    denikar New Member

    Joined:
    Feb 8, 2013
    Location:
    Canton, MI
  6. wjcandee

    wjcandee Wise One

    Joined:
    Apr 27, 2012
    Location:
    New York, NY
    The third page of this pdf has a diagram and a table that may be helpful. You measure, according to it, from the interior portion of the vertical pipe on the p-trap (the weir is where it tips over to the horizontal) TO the closest portion of the vent pipe. The top right diagram on the third page of the document makes it clearer. 3" pipe has a minimum 6" trap arm.

    http://www.klickitatcounty.org/building/FilesHTML/pdf/plmbghandout0411.pdf
     
  7. mikeplummer

    mikeplummer Plumber

    Joined:
    Mar 28, 2012
    Location:
    Ontario, Canada
    our code requires a minimum of 2 pipe diam to avoid crown venting
     
Similar Threads: Minimum Trap
Forum Title Date
Plumbing Forum, Professional & DIY Advice P-Trap to vent minimum, Weir to Vent question Aug 23, 2013
Plumbing Forum, Professional & DIY Advice Minimum distance from trap to sani-tee Mar 26, 2011
Plumbing Forum, Professional & DIY Advice trap tailpiece minimum length Feb 8, 2011
Plumbing Forum, Professional & DIY Advice Minimum trap arm length? Apr 17, 2010
Plumbing Forum, Professional & DIY Advice Minimum Trap Arm? Feb 4, 2010

Share This Page