Main Service Panels separate neutrals but multiple grounds in bus bar

Discussion in 'Electrical Forum discussion & Blog' started by Mr_Magoo, Sep 21, 2008.

  1. Mr_Magoo

    Mr_Magoo New Member

    Messages:
    16
    I just want to confirm that in my main service panel I am suppossed to put the neutrals in individual holes of the bus bar but multiple (2 or 3) grounds can go in an individual hole. Is this correct?

    Thanks,
    Mike
  2. Alectrician

    Alectrician DIY Senior Member

    Messages:
    689
    No

    Service panel:
    Grounds and neutrals on same bus.
    ONE neutral per hole
    Multiple grounds per hole if the bus is listed for multiple grounds.

    Panels other than service panels ("sub panels"):
    ONE neutral per hole
    Multiple grounds per hole if the bus is listed for multiple grounds
    Neutral bus isolated from ground bus.
  3. Mr_Magoo

    Mr_Magoo New Member

    Messages:
    16
    Thank you. I worded my question poorly and you confirmed my understanding of one neutral per hole. How would I know if the bus bar is rated for multiple grounds per hole? It is a SquareD Homeline Entrance Panel. I don't think there are enough holes in the bus bar for each ground and each common to get their own hole.

    Thanks,
    Mike
  4. maintenanceguy

    maintenanceguy In the Trades

    Messages:
    107
    Location:
    Pennsylvania
    I've never seen any rating that mentioned multiple wires in each hole. If you've run out of space for ground wires, you can get add a lugs from an electrical supplier.

    And Alectrician is right, the netural and ground are bonded together at the main panel but not at any sub panels to avoid return current from sub panels from using the ground as a neutral return path. But around here, the grounds are all terminated on the grounding bus bar and the neutrals are all terminated on the neutral bus bar but the neutral bus bar is just bonded to the panel with an optional screws that's included with the panel.
  5. pudge565

    pudge565 New Member

    Messages:
    24
    Normally if it is rated for 2 grounds per hole it will be egg shaped and not round. You are only allowed 2 per hole if properly rated. No more than that.
Similar Threads: Main Service
Forum Title Date
Electrical Forum discussion & Blog Main lug as a primary service panel Jan 5, 2008
Electrical Forum discussion & Blog 50 amp main breaker panel? No such animal Mar 26, 2014
Electrical Forum discussion & Blog What make/model box is this? Is it even a main or is it a sub panel? Jan 19, 2014
Electrical Forum discussion & Blog Wires from Main panael to Subpanel in two separate raceways? Aug 15, 2013
Electrical Forum discussion & Blog Grounding Rod for Main Panel Apr 26, 2012

Share This Page