Lav vent as trap arm?

Discussion in 'Remodel Forum & Blog' started by metlc, Mar 13, 2005.

  1. metlc

    metlc New Member

    Joined:
    Feb 13, 2005
    I'm replacing a lav sink with a new pedestal lav. The toilet drain runs 12 inches from the 3" closet ell to the main 4" stack. I would like to run a five-foot-long trap arm from the new lav trap, tied into this 12" connection at the stack, which itself is not directly accessible. On one hand, this would seem to be "horizontal wet venting," which is supposedly verboten.

    On the other hand, Section 1002.1 of the 2001 California Plumbing Code says: "Each fixture trap shall have a protecting vent so located that the developed length of the trap arm from the trap weir to the inner edge of the vent shall be within the distance given in Table 10-2...."

    Table 10-2 lists, for a 2" trap arm, a Trap to Vent Distance of five feet.

    So..............? Would that make it OK?
     
  2. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    vent

    Usually this would be considered connecting to the "closet bend" which is not permitted. In addition, you still need a vent on the lavatory drain, and you cannot install the "P" trap under the floor.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
Similar Threads: vent trap
Forum Title Date
Remodel Forum & Blog Closet vent from vertical? Aug 13, 2015
Remodel Forum & Blog Bathroom ventilation - multiple fans to one 4" eave vent duct Jan 20, 2015
Remodel Forum & Blog how to insert a charcole filter on vent pipe Apr 29, 2014
Remodel Forum & Blog Bathroom remodel with wall hung toilet. Need advice on plumbing and venting. Mar 10, 2014
Remodel Forum & Blog Skim coated paneling now cracking after a year. Would eave vents help? Jan 23, 2014

Share This Page