Does the stack vent count as a vent for the toilet since it’s within 4’? Or do the upstream fixtures kill the vent ?
 

Tuttles Revenge

In the Trades
Messages
4,252
Reaction score
1,487
Points
113
It depends on what that 2" pipe is doing on the Run of the wye. Is that going up to a bathroom sink, tub/shower that is vented using proper horizontal venting? Then yes, it would be vented.

It looks like that stack connection is a double wye for use in back to back toilet scenarios. which typically dont work for venting, but since toilets don't rely on venting as a means of trap seal maintenance it does work as venting and cross flow.
 

Jeff H Young

In the Trades
Messages
8,991
Reaction score
2,251
Points
113
Location
92346
Agree the 2 inch is key to this issue the w/c wouldn't be a problem however if the 2 inch is simply a trap arm for a tub or shower and not a wet vet vent then its a no go.
 

Omolo

New Member
Messages
14
Reaction score
0
Points
1
Location
Ohio
agree the 2 inch is key to this issue the w/c wouldnt be a problem however if the 2 inch is simplky a trap arm for a tub or shower and not a wet vet vent then its a no go.
It’s a shower line that does jump up but is vented off of a tee in the wall
 