Is there enough power here

Discussion in 'Electrical Forum discussion & Blog' started by DIY, Jul 19, 2009.

  1. DIY

    DIY Member

    Dec 24, 2006
    I want to install 3 new window a/c units. 2 - at 5,000 BTU , 1 - at 10,000 or perhaps 12,000 BTU. The service in this place is 100amp. My question is if 2 or 3 a/c units were on at the same time would this cause breaker(s) to trip?

    The 2- 5,000 BTU units will be in seperate rooms plugged into standard 110 receptacles in each room. Each of the 2 rooms that the a/c will be plugged into also controls other outlets and lights on that same circuit. (i have not looked yet but i am sure each room(s) is on either a 15 or 20amp breaker)

    The 10 to 12,000 BTU unit would be plugged into a dedicated circuit or it might have one maybe two other things on it (light, ceiling fan)

    Any other information needed to work this out correctly let me know!

    Thanks to all!
  2. Alectrician

    Alectrician DIY Senior Member

    Jun 15, 2007
    If you are running new circuits for the AC's, no problem. If you want to plug them into existing circuits, you may have a problem. It depends on what elese is on the existing circuit(s).
  3. Sponsor

    Sponsor Paid Advertisement

  4. jimbo

    jimbo Plumber

    Aug 31, 2004
    San Diego
    Off the cuff, the 5k BTU unit may draw something like 5 amps, and a 10 or 12K btu unit....around 8 to 9. Obviously you could not run any two of these on one circuit, but it each was on a separate breaker, you would be all right. But anything like a microwave, hair dryer, or large audio vidio set up, mixed with the A/C, could put any circuit over.
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Sep 2, 2004
    Retired Systems engineer for defense industry.
    New England
    It somewhat depends on what else is in the house that's a big electrical load. Older refrigerators, electric stove, electric dryer, electric water heater. If everything was on at the same time, you might blow the main breaker.
  6. Thatguy

    Thatguy Homeowner

    Aug 27, 2008
    A bounty hunter like in "Raising Arizona"
    5000 BTU/hr at COP = 3 = 500w = 4A at 120v.
    10K BTU = 8A
    If they all start at the same time you may have a problem.
  7. Scuba_Dave

    Scuba_Dave Extreme DIY Homeowner

    Jan 5, 2009
    Used to be in IT
    South of Boston, MA
    I had a 24k & a 12k on a 100a service without a problem plus a 50a hot tub
    But I had gas heat, cooking, stove & dryer
Similar Threads: enough power
Forum Title Date
Electrical Forum discussion & Blog Not enough amps for Toto Neorest/Now what? Jan 4, 2010
Electrical Forum discussion & Blog tester prongs not long enough? Sep 9, 2008
Electrical Forum discussion & Blog New siding, lost power to 2nd floor Sep 16, 2015
Electrical Forum discussion & Blog Temporary power panel Aug 5, 2015
Electrical Forum discussion & Blog Lost Power to Detached Garage Apr 8, 2015

Share This Page